[Equest-users] loop flow

B. Fountain bfountain at greensim.com
Thu Aug 27 06:16:12 PDT 2009


Try setting your loop sizing to primary rather than secondary.  Primary
sizes the loop based on the chiller capacity -- good if your primary
equipment sizing is known.  Secondary sizes the loop based on the coils
attached to the loop -- good if you are autosizing your equipment.  The
default is secondary.



> Hi all,
>
>
>
> As I know the capacity of my chiller, condenser and boiler I try to
> allocate the value in the detailed mode. This is working fine but in the
> PV-A report I can see that for example the chiller has the allocated
> capacity but the flow of the chilled water loop and the flow through the
> chiller is different. How can this happen ? I mean I have a single
> system pump it is one loop the chiller is directly connected to the
> chilled water loop ( mass conservation ? ). When I want to allocate a
> capacity to my condenser I always get the error message
>
>
>
> ***ERROR****************************************************************
> *******
>
>              Pump: CW Loop Pump                     has zero design
> flow.  If attached to
>
>              a DHW loop, make sure the recirculation flow is
>
>              nonzero.
>
>
> But I connected the loop to the chiller and I put a temperature
> difference, there should be a flow ? I attach also a screen shot from my
> water side set up I hope someone can help me.
>
> Thanks a lot.
>
> Verena
>
>
>
>
>