[Equest-users] Baseboard HW vs.HW Fan Coil
David S Eldridge
DSE at grummanbutkus.com
Wed Aug 12 16:10:45 PDT 2009
You didn't mention in the post, but if the motivation for the study was to compare an existing baseboard system controlled by an outdoor reset schedule to an HVAC system controlled by thermostats, then the savings could be dramatic.
50% sounds like a lot - maybe verify that you have a reasonable reset schedule in your base case, and also that the modeled existing base case has reasonable summer heating usage. The actual baseboard system may be deactivated over the summer, if the modeled baseboards are available throughout the year the savings between the two cases could be exaggerated.
David
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Schmit
Sent: Wednesday, August 12, 2009 12:18 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseboard HW vs.HW Fan Coil
When changing my HVAC system from Baseboard HW to HW Fan Coil, I am seeing ~50% reduction in annual gas usage. The savings seems to be overly high. Has anyone else had any luck comparing the two? What results did you see?
Thanks-
Nick Schmit
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090812/0ae20af5/attachment-0002.htm>
More information about the Equest-users
mailing list