Fri Aug 14 13:48:29 PDT 2009
Verena,
If we’re looking at the same thing, I think the system schematic view might be hard-coded to say “2-pipe coil”. Regardless, it should behave as a 4-pipe IU if you create separate HW and CHW loops and assign both to the IU. If you’re using v3.63, immediately below the 2-pipe label it shows separate heating and cooling coils as expected for a 4-pipe system. The two loops will operate independently to maintain space temperatures.
To verify, you can compare your set up to the example template for a 4-pipe system:
· Search for “Four-Pipe” in Help
· Choose the search result “SYSTEM Type = IU”
· On the right side of the window, scroll down to the bottom of the help content and you’ll see a link labeled “Input template for a standard 2- and 4-pipe IU unit”.
You’ll note that a 2-pipe IU would require a single loop created specifically as TYPE = PIPE-2. The same loop would then be designated as the IU’s cooling and heating loop. It is my understanding that creating two separate heating and cooling loops, without specifying them as 2-PIPE, and assigning both to your IU makes it a 4-pipe.
Thanks,
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Verena Kindl [mailto:kindl at scholze.de]
Sent: Friday, August 14, 2009 3:07 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 4-pipe IU
Hi,
i finally model my system as an induction unit with a 4 pipe coil. As it is not possible in the wizard I do it in the detailed edit. But even I choose for the loop always the CHW / HW and not the 2 pipe option I always see a 2 pipe coil on the screen. How can I activate the 4 pipe coil ?
Thanks Verena
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090814/e2f752a6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090814/e2f752a6/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090814/e2f752a6/attachment-0002.jpeg>
More information about the Equest-users
mailing list