Ryan,
Your assumption is correct. The layer you’re referring to represents the combined batt insulation and framing type specified in the wizard. The layers shown in the detailed interface are continuous layers, so non-continuous constructions need to be converted to an equivalent continuous construction.
More specifically, eQUEST is applying the framing factors found in Standard 90.1 Table A9.2B. For example, specifying metal 2x6 studs 24” OC with R-19 batt in the wizard would correspond to a “self-named” layer showing thermal resistance R-8.6 in the detailed interface. You can locate this same conversion in Table A9.2B (page 105 of the 2004 edition).
Thanks,
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Ryan Schmidt [mailto:RSchmidt at Horizon-Engineering.com]
Sent: Tuesday, August 18, 2009 7:07 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Equest-generated Construction Materials
After the Wizard Mode is completed, construction layers are formed for the various external surfaces based on the designated insulation and construction types. What does the “self-named” material correspond to (such as material “E2 EWall Cons Mat 2 (0.91)”)? I would assume that depending on the framing or construction method, equest would generate a derating factor to account for discontinuities in insulation, etc. However the “self-named” material improves the overall u-value for the composition. What does this layer correspond to and can it be omitted when redefining the layers in Detail Mode? Thanks in advance for your help.
Ryan G. Schmidt
Horizon Engineering Associates, Field Engineer
rschmidt at horizon-engineering.com <mailto:rschmidt at horizon-engineering.com>
704.523.5354 (t)
704.523.5347 (f)
252.622.9606 (m)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090818/12100060/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090818/12100060/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090818/12100060/attachment-0002.jpeg>
More information about the Equest-users
mailing list