[Equest-users] Heat recovery chiller
Molly Curtz
molly.curtz at arup.com
Mon Aug 24 15:56:57 PDT 2009
Eric,
I was working on a similar problem a while ago. I was unable to find any way to control the heat recovery chiller operation based on the Hot Water Loop loads (chillers would only sequence on the chilled water loop load). I ended up going the route of manipulating hourly results data in a spreadsheet.
Good Luck, and if you do determine a way to accomplish this, please post to report.
Regards,
Molly Curtz, P.E.
Mechanical Engineer
Arup
403 Columbia St., Suite 220
Seattle, WA 98104
direct: 206 493 2234
tel: 206 749 9674 ext. 25534
fax: 206 749 0665
molly.curtz at arup.com
www.arup.com <http://www.arup.com/>
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eric O'Neill
Sent: Friday, August 21, 2009 6:39 AM
To: Xavier Garcia Casals
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat recovery chiller
Thanks for the response Xavier,
The cooling load is 24/7 and is located in an interior zone of a building located in a cold climate, so there are simultaneous heating and cooling periods. What I'm hoping to create is a system that will act much like a boiler, in that whenever the HW loop needs heat, the HTREC chiller runs and provides heat while cooling the chilled water loop. I added the HTREC chiller because it's supposed to be able to supply higher condensing water temperatures (which I need for my HW loops) than my other boilers are. The DOE2.2 documentation leads me to believe that this chiller would automatically sequence on whenever there is a heating load on the loop, but this doesn't seem to be the case. Even if I delete the HTREC chiller and make my other three chillers recover heat to the HW loop, none of them do.
The coils on the condensing loop are for the waterside economizer. There is more than sufficient heat for heat recovery (cooling load>>heating load), so I still need an economizer, although I want it to be secondary. I don't know if I can sequence that. My guess now after thinking about it is that the system is economizing whenever there is a heating load, so the chillers don't sequence on. Is there a way to make the chillers run if there is a load on the HW loop, but economize the remainder?
Eric
From: Xavier Garcia Casals [mailto:xgcasals at telefonica.net]
Sent: Friday, August 21, 2009 3:20 AM
To: Eric O'Neill
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat recovery chiller
Hi Eric,
Are you sure your heating load is simultaneous with the cooling load (is not enough to have cooling load all the year arround if it does not coincidence in time with the heating load: Chiller off)?. Also, did you check that when there is heating load the Htrc chiller is scheduled before than the other 3 chillers you have? Otherwise would be impossible to recover heat. What about those coils you have on the condensing loop? Aren't they taking away the heat you want to recover from the condenser?
En/na Eric O'Neill ha escrit:
All,
I'm trying to model a hot water loop that's being heated entirely by a heat recovery chiller (htrec) and supplying heating to a VAV system. I'd like to utilize condenser heat prior to rejection to the dry coolers (I have a large cooling load year around). The trouble is, even though it appears like it is set up correctly, the system doesn't want to reject ANY heat to the HW loop. When I just created the loop and ran a simulation, eQuest gave me an error saying I had no primary heat source on the HW loop. I tried adding a dummy boiler with virtually no capacity, and that got rid of the error and allowed me to run, but I still had no heat going to my HW loop.
Has anyone had success with this? When reading the DOE2.2 dictionary, it appears this is exactly what the htrec chiller was designed to do, but nothing I change makes any difference. If anyone's willing, I can send you a copy of my input and pd2 files to look at.
Thanks,
Eric O'Neill
Mechanical Engineer, LEEDAP
Michaels Engineering
400 Main Street, Ste 200
La Crosse, WI 54601
direct: 608-785-3328
main: 608-785-1900
fax: 608-784-2270
elo at michaelsengineering.com
http://www.michaelsengineering.com
<<Water Loops.png>> <<Heat Recovery Setup.png>>
________________________________
________________________________
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Xavier García Casals
Tel: (+34) 91 843 19 85
Móvil: 660 22 94 45
xgcasals at telefonica.net
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090824/df38752a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 26673 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090824/df38752a/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 36512 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090824/df38752a/attachment-0005.png>
More information about the Equest-users
mailing list