[Equest-users] Cooling Coil Error
Jonathan Curtin
jcurtin at WylieAssociates.com
Thu Dec 17 10:00:00 PST 2009
Jason,
My bet is that you have a pretty high dT across the fan (operating at >
5") causing your actually leaving air temperature off the cooling coil
to be less than 50F. I am pretty sure (although it has been a while)
that you can avoid this error and still maintain the same conditions if
you implement a reset schedule on your air temperature (even if you
don't actually reset it), rather than using the cool-min-temp only.
Regards,
Jonathan M. Curtin, EIT, LEED(r) AP
Mechanical Engineer
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason
Wendel
Sent: Thursday, December 17, 2009 11:50 AM
To: 'equest-users at lists.onebuilding.org'
Subject: [Equest-users] Cooling Coil Error
I have an error that says:
In S1 Sys (VAVS), Cooling coil leaving temperature must be at least 6F
higher than entering water temp.
I have 44" entering CHW with a 12 degree delta T. Cold Air for the
system is set to 54F. I thought with a chiller with a 12 degree delta T
there shouldn't be the above error.
Any ideas?
-Jason
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------------------------------------------------------
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091217/90e3195a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091217/90e3195a/attachment-0002.jpeg>
More information about the Equest-users
mailing list