[Equest-users] IPLV in Heat Pumps
David S Eldridge
DSE at grummanbutkus.com
Mon Dec 21 07:27:56 PST 2009
eQuest automatically calculates part load performance based on the rated condition (COP in your case) and the performance curves that modify the power consumption based on temperature and part-load (and other factors for other equipment...water temperatures, etc.).
If you input IPLV where eQuest is expecting a COP, you'll be underestimating the power consumption from the units. These inputs will often be in the form of "Energy Input Ratio", or EIR for many types of eQuest equipment which is the inverse of COP.
If you need to verify the part-load performance that will be calculated, you can use hourly reports to verify that using the COP and default performance curves gives a reasonable result.
As others mentioned, the IPLV references a specific set of weather and load, applied to the piece of equipment. The average annual efficiency will vary based on your actual weather and load on the unit.
David
http://www.grummanbutkus.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Amandeep Singh
Sent: Thursday, December 17, 2009 3:04 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] IPLV in Heat Pumps
Hello everyone,
I was working on a school model located in Lakeside, San Diego county. The school has Bard wall mount heat pumps (capacity - 2 to 4 tons), really old one. I got manufacture data of the old and new units for replacement. The new units data has EER, IPLV and COP ratings. I would prefer to use IPLV instead of EER rating in case of cooling to calculate savings. The eQuest does have options for EER and SEER but not for IPLV in the schematic design wizard. What should I do here?
Does it make sense to use IPLV instead of EER to calculate savings for the Lakeside?
Thanks,
Aman
[cid:image001.jpg at 01CA7F35.80DA39E0]
Amandeep Singh
Energy Engineer
8690 Balboa Ave, Suite 100
San Diego, CA 92123-1502
858.634.4729 phone
858.244.1178 fax
www.energycenter.org<http://www.energycenter.org/> web
Submit your SANDEE Award nomination today.
Visit www.energycenter.org<http://www.energycenter.org/signature>.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091221/72de34e7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 8634 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091221/72de34e7/attachment-0002.jpg>
More information about the Equest-users
mailing list