[Equest-users] OK - you East Coast Gurus !!!
rongxinyin
rongxinyin1 at gmail.com
Wed Feb 18 23:29:56 PST 2009
I agree. Once you go back from the custom window and change some value such as floor height, multiplier, etc, the custom window would disappear. You have to define the custom window for each floor, ground, mid, and top.
Goodluck!!!!!!!!!!!!!!
Rongxin
2009-02-18
rongxinyin
发件人: Hwakong Cheng
发送时间: 2009-02-18 22:57:35
收件人: 'John Aulbach'; bfountain at greensim.com; 'Steve Mignogna'
抄送: equest-users
主题: Re: [Equest-users] OK - you East Coast Gurus !!!
John,
When you use custom windows, you have to define them for each of the ground, mid, and top floors, regardless of whether you use the floor multipliers. In the custom window placement dialogue box, there are radio buttons hidden in the upper left corner for each of these. Step through the mid and top level facades and that should do the trick.
The west is the best...
Hwakong
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Wednesday, February 18, 2009 10:13 PM
To: bfountain at greensim.com; Steve Mignogna
Cc: equest-users at lists.onebuilding.org
Subject: [Equest-users] OK - you East Coast Gurus !!!
I am working late on the West Coast and not solving my problem. I also need to upgrase my computer memory to 4 gB. I am using my home machine, and forgot how nice 2 gB were. I cannot even rotate this building in 3-D
I am doing a large condo project, and am attempting to use floor multipliers. I leave the Floor Mulipliers check box checked and develop my floor, including precise window locations (which can be lost if a single point in Shell or Zone is moved).
The 3-D display in this mode shows, of course, bottom floor, mid floor, and top floor. But the window locations were not carried into the mid and top floors.
I then tried unchecking the Floor Multiplier box. Wa -La !! The precise shell and zoning pattern is displayed. But again, the correct window patterns are incorrect !!
I would love to wake up tomorrow with an answer in my inbox.
I'd even root for the Yankees or Red Sox for you.
Well, maybe that is too extreme.
Thank you
John Aulbach
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090218/de635023/attachment-0002.htm>
More information about the Equest-users
mailing list