[Equest-users] MIN-AIR-SCH and -999
Brahme, Rohini UTRC
BrahmeR at utrc.utc.com
Mon Jan 19 08:22:39 PST 2009
There was a post some time back on how to incorporate -999 in the
Min-Air-Sch. Any resolution on that? The schedule type fraction does not
allow for -999, and the min-air-sch seems to take only sch of type
fraction as input. Following is the info from the help file
Thanks,
-Rohini
MIN-AIR-SCH
Takes the U-name of a SCHEDULE that contains hourly values of the ratio
of minimum outside air flow to supply air flow. Values in the
MIN-AIR-SCH vary from 0.0 (no outside air flow; economizer inactive if
specified) to 1.0 (100% outside air flow). A value of 0.001 actives the
economizer. A value of -999 returns the hourly value to MIN-OUTSIDE-AIR
or to the program's calculated minimum outside air value (found on
report SV-A for the SYSTEM or for each zone for zonal systems). During a
warmup period, this schedule is normally set to zero and can then be set
to -999 during other hours to allow the specified or calculated
ventilation minimum damper position to be used. Note that schedules are
ignored in the design routines; therefore, the minimum ventilation air
desired for design must be specified either at the zone or system level.
More information about the Equest-users
mailing list