[Equest-users] NINJA-SPAM: Which report tells me how Space Cooling is divided up?
Kendra Tupper
ktupper at rmi.org
Thu Jan 8 09:07:57 PST 2009
The values in the Loads reports represent the end use contribution of
cooling loads, not energy consumed to meet those cooling loads. The BEPS and
BEPU reports show end use energy consumption and include the effects of
equipment efficiency, etc.
As Vikram pointed out, the Loads reports do not include ventilation loads,
which is a significant portion of the cooling loads has anyone ever
figured out a way to get the load breakdown including the OA contribution?
Perhaps from custom hourly reports?
On 1/8/09 10:03 AM, "Lam, Linda" <linda.lam at wspfk.com> wrote:
> Vikram,
>
> The total MBTU used for cooling from the LS-F report does is much greater than
> the space cooling enduse value in the BEPS report. Does the total MBTU in LSF
> represent all energy including (heat rejection, pumps and ventilation fans)
> associated with cooling the building? Thanks for your help!
>
> LS-F Report:
>
>
> BEPS report:
>
>
>
>
>
> From: Vikram Sami [mailto:VSami at lasarchitect.com]
> Sent: Thursday, January 08, 2009 8:49 AM
> To: Lam, Linda; equest-users at lists.onebuilding.org
> Subject: RE: NINJA-SPAM:[Equest-users] Which report tells me how Space Cooling
> is divided up?
>
> Linda,
>
> LS-F gives you the building monthly load components for cooling and heating.
> LS-C gives you the building peak load components.
>
> LS-E & LS-B give you the space loads
>
> NOTE: These reports do not include the ventilation loads I think those are
> added at the system level.
>
> Vikram Sami, LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
> LORD, AECK & SARGENT ARCHITECTURE
> 1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
> Responsive Design · Technological Expertise · Exceptional Service
> Please visit our new website | www.lordaecksargent.com
> <file:///\\www.lordaecksargent.com\>
> P Think GREEN before you print.
>
>
>
> From: equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lam, Linda
> Sent: Thursday, January 08, 2009 11:42 AM
> To: equest-users at lists.onebuilding.org
> Subject: NINJA-SPAM:[Equest-users] Which report tells me how Space Cooling is
> divided up?
>
>
> Dear eQuest Users
>
>
>
> Does anyone know which report will tell me how Space Cooling is divided up?
> ie, cooling energy attributed to envelope loads, lighting loads and equipment
> loads.
>
>
>
> Thanks!
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090108/e88a0240/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 237878 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090108/e88a0240/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 119247 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090108/e88a0240/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 266 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090108/e88a0240/attachment-0002.png>
More information about the Equest-users
mailing list