[Equest-users] Equipment Sizing and % Hrs in Throttling Range
Karen Walkerman
kwalkerman at gmail.com
Sun Jan 18 04:49:38 PST 2009
we need the inp files too!
On Sat, Jan 17, 2009 at 5:59 PM, Mathew Higgins <higgins at edi-arch.com>wrote:
> All - I'm trying to resolve a gshp school system model, to reduce the
> number of hours outside of throttling range for LEED purposes. I have
> scowered multiple threads talking about sizing, throttling range, min air
> flow ratios, reverse-action TSTATs, night-setback, gshp's, etc. and have
> applied suggestions with minimal result. The only way I can take
> considerable hours out of the % not in throttling range is if I increase
> sizing ratios way beyond design capacities and strip out everything that
> makes the model accurately reflect design conditions.
>
> I've attached the before and after (.pd2) files for reference, however
> results are still not seen. SS-R reports indicate hours in the 100+ load
> range, but again this is going beyond manually specifying capacities and
> using sizing ratios. Also to be noted, the ASHRAE baseline (Pkg Elec HP) is
> also in the same range and is not responding to changes... which would
> suggest something common to both within Appendix G criteria.
>
> Experience and opinions would be greatly appreciated.
>
> --
> Matthew Higgins, LEED AP + ASHRAE-HBDP
> Technical Specialist
> Environmental Dynamics, Inc.
> Architecture and Sustainability Consulting Services
> 505.242.2851
>
> Any data provided by the Consultant, verbal or written, are to be
> considered opinions of building energy and/or daylight performance. The
> Client understands that the Consultant has no control of occupant habits,
> equipment or material performance or characteristics, site or climate
> conditions or the Contractor's method of assembly, and that the Consultant's
> opinions regarding building energy/daylight performance are made on the
> basis of the Consultant's professional judgment and experience. The
> Consultant makes no warranty, express or implied, that the energy/daylight
> performance of the building will not vary from the Consultant's opinion of
> building energy/daylight performance.
>
>
> Proj "0849-APS Phase II 12-10-08 proposed"
> ProgramVersion = "eQUEST 3.62.6236"
> BDBaseVersion = 22
> ProductCode = "eQUEST"
> WeatherFile = "TMY2\ALBUQUNM.bin"
> CreateDate = 1228503283
> ModDate = 1232225796
> RunDate = 1229102015
> LibraryFile = "eQ_Lib.dat"
> ActiveMode = 0
> InputModule = 3
> UseCameraData = 1
> ClippingRange = ( 131.756, 454.319 )
> FocalPoint = ( 84.0581, 154.325, 10.2624 )
> Position = ( -79.2852, -62.439, 49.6857 )
> ViewUpVector = ( 0, 0, 1 )
> ViewAngle = 25.3151
> InterfaceMode = 1
> AllowWizard = 1
> NotProjFile = "0849-APS Phase II 12-10-08 proposed"
> InputUnitsType = "English"
> OutputUnitsType = "English"
> PreviousName = "0849-APS Phase II 12-10-08 proposed"
> DetailedModelEdits = 1
> ProjTreeType[2] = 1
> ProjTreeType[3] = 1
> ProjTreeType[4] = 1
> ProjTreeType[5] = 1
> ProjTreeID[2] = 10080000
> ProjTreeID[3] = 10080062
> ProjTreeID[4] = 10670000
> ProjTreeID[5] = 10550000
> ProjTreeLabel[2] = "Common LTWL ML Spc (ML.C1)"
> ProjTreeLabel[3] = "EL1 SSE Perim Plnm (G.SSE63)"
> ProjTreeLabel[4] = "Domestic Water Heater"
> ProjTreeLabel[5] = "EL1 WSW Perim Pl Zn (G.WSW78)"
> BDBUpdateReEval = 0
> ..
>
> MainWiz "0849-APS Phase II 12-10-08 proposed"
> ProductCode = "eQUEST"
> WizardType = "Design Development"
> DebugID = 0
> AllowCustWinDoor = 1
> ScreenIDArrIdx = 6
> ScreenIDArrID = 250
> Coverage = "All eQUEST Locations"
> State = "New Mexico"
> Location = "Albuquerque"
> BldgType = "School, K-6 Elementary"
> ..
>
> ShellWiz "Phase II"
> ModelEnduse[3] = 0
> ModelEnduse[4] = 0
> ModelEnduse[5] = 0
> ModelEnduse[12] = 0
> ModelEnduse[13] = 1
> ScreenIDArrIdx = 1
> ScreenIDArrID = 22
> BldgType = "School, K-6 Elementary"
> GrossArea = 11008
> Footprint = "- custom -"
> FlrToFlr = 12.5
> ZoningPattern = "- custom -"
> NumMCZnGrps = 0
> DiagLink = "Bldg Envelope & Loads 1 Diag Data"
> RoofInsulLocation = "Roof Surface"
> CeilingConsType = "Lay-In Acoustic Tile"
> GrndFlrConsType = "4 in. Concrete"
> GrndFlrInsType = "vert ext bd, R-5, 2ft deep"
> GrndFlrSecInsType = "Vinyl Tile"
> ZoningCurrent = 1
> NumFloorVertices = 53
> FloorVertX[1] = 6.85
> FloorVertX[2] = 46.5
> FloorVertX[3] = 46.5
> FloorVertX[4] = 46.5
> FloorVertX[5] = 46.5
> FloorVertX[6] = 46.5
> FloorVertX[7] = 46.5
> FloorVertX[8] = 46.5
> FloorVertX[9] = 42.65
> FloorVertX[10] = 42.6
> FloorVertX[11] = 42.7
> FloorVertX[12] = 42.65
> FloorVertX[13] = 46.5
> FloorVertX[14] = 46.5
> FloorVertX[15] = 46.5
> FloorVertX[16] = 46.5
> FloorVertX[17] = 55.55
> FloorVertX[18] = 78.9
> FloorVertX[19] = 89.3
> FloorVertX[20] = 113.15
> FloorVertX[21] = 114.65
> FloorVertX[22] = 123.1
> FloorVertX[23] = 121.6
> FloorVertX[24] = 145.9
> FloorVertX[25] = 161.75
> FloorVertX[26] = 137.45
> FloorVertX[27] = 133.2
> FloorVertX[28] = 123.8
> FloorVertX[29] = 100.35
> FloorVertX[30] = 95.65
> FloorVertX[31] = 90.5
> FloorVertX[32] = 67.55
> FloorVertX[33] = 61.45
> FloorVertX[34] = 46.5
> FloorVertX[35] = 46.5
> FloorVertX[36] = 17.5
> FloorVertX[37] = 17.45
> FloorVertX[38] = 17.45
> FloorVertX[39] = 17.4
> FloorVertX[40] = 17.45
> FloorVertX[41] = 17.5
> FloorVertX[42] = 13.1
> FloorVertX[43] = 6.8
> FloorVertX[44] = 6.8
> FloorVertX[45] = 6.8
> FloorVertX[46] = 17.45
> FloorVertX[47] = 17.45
> FloorVertX[48] = 17.4
> FloorVertX[49] = 17.45
> FloorVertX[50] = 17.45
> FloorVertX[51] = 17.5
> FloorVertX[52] = 6.85
> FloorVertX[53] = 6.85
> FloorVertY[1] = 35.45
> FloorVertY[2] = 35.45
> FloorVertY[3] = 56.45
> FloorVertY[4] = 67.45
> FloorVertY[5] = 92.8
> FloorVertY[6] = 117.8
> FloorVertY[7] = 129.3
> FloorVertY[8] = 155.15
> FloorVertY[9] = 155.15
> FloorVertY[10] = 164.5
> FloorVertY[11] = 167.05
> FloorVertY[12] = 175.85
> FloorVertY[13] = 175.9
> FloorVertY[14] = 201.9
> FloorVertY[15] = 213.2
> FloorVertY[16] = 236.1
> FloorVertY[17] = 232.15
> FloorVertY[18] = 222
> FloorVertY[19] = 217.45
> FloorVertY[20] = 207.05
> FloorVertY[21] = 210.55
> FloorVertY[22] = 206.85
> FloorVertY[23] = 203.35
> FloorVertY[24] = 192.75
> FloorVertY[25] = 229.1
> FloorVertY[26] = 239.7
> FloorVertY[27] = 229.95
> FloorVertY[28] = 234.05
> FloorVertY[29] = 244.3
> FloorVertY[30] = 246.3
> FloorVertY[31] = 248.55
> FloorVertY[32] = 258.5
> FloorVertY[33] = 261.25
> FloorVertY[34] = 267.75
> FloorVertY[35] = 273.55
> FloorVertY[36] = 273.55
> FloorVertY[37] = 238.2
> FloorVertY[38] = 213.2
> FloorVertY[39] = 207.75
> FloorVertY[40] = 201.8
> FloorVertY[41] = 177.4
> FloorVertY[42] = 177.4
> FloorVertY[43] = 177.4
> FloorVertY[44] = 170.45
> FloorVertY[45] = 153.65
> FloorVertY[46] = 153.65
> FloorVertY[47] = 129.1
> FloorVertY[48] = 123.5
> FloorVertY[49] = 118.2
> FloorVertY[50] = 92.8
> FloorVertY[51] = 67.95
> FloorVertY[52] = 67.95
> FloorVertY[53] = 56.75
> AdiabaticCurrent = 1
> GroundZnGrp[4] = "Exhausted Zone Group 2"
> GroundZnGrp[12] = "Exhausted Zone Group 2"
> GroundZnGrp[13] = "Unconditioned Zone Group 4"
> GroundZnGrp[14] = "Exhausted Zone Group 2"
> GroundZnGrp[16] = "ERV Zone Group 3"
> GroundZnGrp[25] = "EL1 Ground Floor"
> GroundZnGrp[32] = "ERV Zone Group 3"
> ZoneGroupsOK = 1
> DfltZnGrpName = ( "EL1 Underground Areas", "EL1 Ground Floor",
> "EL1 Ground Floor", "EL1 Typical Floor(s)",
> "EL1 Typical Floor(s)", "EL1 Top Floor",
> "EL1 Top Floor" )
> CustomFootprint = 1
> CustomZoning = 1
> ActiveZoneIndex = 62
> FloorArea = 11008.1
> FloorPerimLen = 840.296
> LastFootprint = 5
> OverhangOption = "None"
> GTCCategory[2] = "- select another -"
> PercentGlass2[1] = 0
> PercentGlass3[1] = 20
> NumExtDoors1[1] = 0
> NumExtDoors2[1] = 0
> NumExtDoors3[1] = 0
> DoorWidth[1] = 3
> OpaqueDoorType[1] = "Steel Hollow core w/o Brk"
> SkyZonesCurrent = 1
> SkyltZones[1] = 1
> SkyltZones[2] = 1
> SkyltZones[3] = 1
> SkyltZones[4] = 1
> SkyltZones[5] = 1
> SkyltZones[6] = 1
> SkyltZones[7] = 1
> SkyltZones[8] = 1
> SkyltZones[9] = 1
> SkyltZones[10] = 1
> SkyltZones[11] = 1
> SkyltZones[12] = 1
> SkyltZones[13] = 1
> SkyltZones[14] = 1
> SkyltZones[15] = 1
> SkyltZones[16] = 1
> SkyltZones[17] = 1
> SkyltZones[18] = 1
> SkyltZones[19] = 1
> SkyltZones[20] = 1
> SkyltZones[21] = 1
> SkyltZones[22] = 1
> SkyltZones[23] = 1
> SkyltZones[24] = 1
> SkyltZones[25] = 1
> SkyltZones[26] = 1
> SkyltZones[27] = 1
> SkyltZones[28] = 1
> SkyltZones[29] = 1
> SkyltZones[30] = 1
> SkyltZones[31] = 1
> SkyltZones[32] = 1
> SkyltZones[33] = 1
> SkyltZones[34] = 1
> SkyltZones[35] = 1
> SkyltZones[36] = 1
> SkyltZones[37] = 1
> SkyltZones[38] = 1
> SkyltZones[39] = 1
> SkyltZones[40] = 1
> SkyltZones[41] = 1
> SkyltZones[42] = 1
> SkyltZones[43] = 1
> SkyltZones[44] = 1
> SkyltZones[45] = 1
> SkyltZones[46] = 1
> SkyltZones[47] = 1
> SkyltZones[48] = 1
> SkyltZones[49] = 1
> SkyltZones[50] = 1
> SkyltZones[51] = 1
> SkyltZones[52] = 1
> SkyltZones[53] = 1
> SkyltZones[54] = 1
> SkyltZones[55] = 1
> SkyltZones[56] = 1
> SkyltZones[57] = 1
> SkyltZones[58] = 1
> SkyltZones[59] = 1
> SkyltZones[60] = 1
> SkyltZones[61] = 1
> SkyltZones[62] = 1
> SkyPosCurrent = 1
> DayZonesCurrent[3] = 1
> DayltZones[1] = 1
> DayltZones[2] = 1
> DayltZones[3] = 1
> DayltZones[4] = 1
> DayltZones[5] = 0
> DayltZones[401] = 1
> DayltZones[402] = 1
> DayltZones[403] = 0
> DayltZones[404] = 0
> DayltZones[405] = 1
> DayltZones[406] = 1
> DayltZones[407] = 1
> DayltZones[408] = 1
> DayltZones[409] = 1
> DayltZones[410] = 1
> DayltZones[411] = 1
> DayltZones[412] = 1
> DayltZones[413] = 0
> DayltZones[414] = 1
> DayltZones[415] = 1
> DayltZones[416] = 1
> DayltZones[417] = 1
> DayltZones[418] = 1
> DayltZones[419] = 1
> DayltZones[420] = 1
> DayltZones[421] = 1
> DayltZones[422] = 1
> DayltZones[423] = 1
> DayltZones[424] = 0
> DayltZones[425] = 1
> DayltZones[426] = 0
> DayltZones[427] = 1
> DayltZones[428] = 1
> DayltZones[429] = 1
> DayltZones[430] = 1
> DayltZones[431] = 1
> DayltZones[432] = 1
> DayltZones[433] = 1
> DayltZones[434] = 1
> DayltZones[435] = 0
> DayltZones[436] = 0
> DayltZones[437] = 0
> DayltZones[438] = 0
> DayltZones[439] = 0
> DayltZones[440] = 0
> DayltZones[441] = 0
> DayltZones[442] = 0
> DayltZones[443] = 0
> DayltZones[444] = 0
> DayltZones[445] = 0
> DayltZones[446] = 0
> DayltZones[447] = 0
> DayltZones[448] = 0
> DayltZones[449] = 0
> DayltZones[450] = 0
> DayltZones[451] = 0
> DayltZones[452] = 0
> DayltZones[453] = 1
> DayltZones[454] = 1
> DayltZones[455] = 1
> DayltZones[456] = 1
> DayltZones[457] = 1
> DayltZones[458] = 1
> DayltZones[459] = 1
> DayltZones[460] = 1
> DayltZones[461] = 1
> DayltZones[462] = 1
> WinDoorCurrent = 1
> DetailsCurrent = ( 1, 1, 1 )
> BDLNumDayltCtrls[1] = 0
> BDLNumDayltCtrls[2] = 0
> BDLNumDayltCtrls[3] = 0
> BDLNumDayltCtrls[4] = 0
> BDLNumDayltCtrls[5] = 0
> BDLNumDayltCtrls[401] = 0
> BDLNumDayltCtrls[402] = 0
> BDLNumDayltCtrls[403] = 0
> BDLNumDayltCtrls[404] = 0
> BDLNumDayltCtrls[405] = 0
> BDLNumDayltCtrls[406] = 0
> BDLNumDayltCtrls[407] = 0
> BDLNumDayltCtrls[408] = 0
> BDLNumDayltCtrls[409] = 0
> BDLNumDayltCtrls[410] = 0
> BDLNumDayltCtrls[411] = 0
> BDLNumDayltCtrls[412] = 0
> BDLNumDayltCtrls[413] = 0
> BDLNumDayltCtrls[414] = 0
> BDLNumDayltCtrls[415] = 0
> BDLNumDayltCtrls[416] = 0
> BDLNumDayltCtrls[417] = 0
> BDLNumDayltCtrls[418] = 0
> BDLNumDayltCtrls[419] = 0
> BDLNumDayltCtrls[420] = 0
> BDLNumDayltCtrls[421] = 0
> BDLNumDayltCtrls[422] = 0
> BDLNumDayltCtrls[423] = 0
> BDLNumDayltCtrls[424] = 0
> BDLNumDayltCtrls[425] = 0
> BDLNumDayltCtrls[426] = 0
> BDLNumDayltCtrls[427] = 0
> BDLNumDayltCtrls[428] = 0
> BDLNumDayltCtrls[429] = 0
> BDLNumDayltCtrls[430] = 0
> BDLNumDayltCtrls[431] = 0
> BDLNumDayltCtrls[432] = 0
> BDLNumDayltCtrls[433] = 0
> BDLNumDayltCtrls[434] = 0
> BDLNumDayltCtrls[435] = 0
> BDLNumDayltCtrls[436] = 0
> BDLNumDayltCtrls[437] = 0
> BDLNumDayltCtrls[438] = 0
> BDLNumDayltCtrls[439] = 0
> BDLNumDayltCtrls[440] = 0
> BDLNumDayltCtrls[441] = 0
> BDLNumDayltCtrls[442] = 0
> BDLNumDayltCtrls[443] = 0
> BDLNumDayltCtrls[444] = 0
> BDLNumDayltCtrls[445] = 0
> BDLNumDayltCtrls[446] = 0
> BDLNumDayltCtrls[447] = 0
> BDLNumDayltCtrls[448] = 0
> BDLNumDayltCtrls[449] = 0
> BDLNumDayltCtrls[450] = 0
> BDLNumDayltCtrls[451] = 0
> BDLNumDayltCtrls[452] = 0
> BDLNumDayltCtrls[453] = 0
> BDLNumDayltCtrls[454] = 0
> BDLNumDayltCtrls[455] = 0
> BDLNumDayltCtrls[456] = 0
> BDLNumDayltCtrls[457] = 0
> BDLNumDayltCtrls[458] = 0
> BDLNumDayltCtrls[459] = 0
> BDLNumDayltCtrls[460] = 0
> BDLNumDayltCtrls[461] = 0
> BDLNumDayltCtrls[462] = 0
> OccShape = ( "EL1 Occup Profile (S1)", "EL1 Occup Profile (S2)",
> "EL1 Occup Profile (S3)" )
> ILShape = ( "EL1 InsLtg Profile (S1)", "EL1 InsLtg Profile (S2)",
> "EL1 InsLtg Profile (S3)" )
> ELElecIntens = 0.2
> ELDayShapes = ( "EL1 ExtLtg DayShape (Jan)",
> "EL1 ExtLtg DayShape (Feb)",
> "EL1 ExtLtg DayShape (Mar)",
> "EL1 ExtLtg DayShape (Apr)",
> "EL1 ExtLtg DayShape (May)",
> "EL1 ExtLtg DayShape (Jun)",
> "EL1 ExtLtg DayShape (Jul)",
> "EL1 ExtLtg DayShape (Aug)",
> "EL1 ExtLtg DayShape (Sep)",
> "EL1 ExtLtg DayShape (Oct)",
> "EL1 ExtLtg DayShape (Nov)",
> "EL1 ExtLtg DayShape (Dec)" )
> OEShape = ( "EL1 OffEq Profile (S1)", "EL1 OffEq Profile (S2)",
> "EL1 OffEq Profile (S3)" )
> CEShape = ( "EL1 CookEq Profile (S1)", "EL1 CookEq Profile (S2)",
> "EL1 CookEq Profile (S3)" )
> MiscShape = ( "EL1 Misc Profile (S1)", "EL1 Misc Profile (S2)",
> "EL1 Misc Profile (S3)" )
> RFDayShapes = ( "EL1 Refrig DayShape (Jan)",
> "EL1 Refrig DayShape (Feb)",
> "EL1 Refrig DayShape (Mar)",
> "EL1 Refrig DayShape (Apr)",
> "EL1 Refrig DayShape (May)",
> "EL1 Refrig DayShape (Jun)",
> "EL1 Refrig DayShape (Jul)",
> "EL1 Refrig DayShape (Aug)",
> "EL1 Refrig DayShape (Sep)",
> "EL1 Refrig DayShape (Oct)",
> "EL1 Refrig DayShape (Nov)",
> "EL1 Refrig DayShape (Dec)" )
> DHWShape = ( "EL1 DHW Profile (S1)", "EL1 DHW Profile (S2)",
> "EL1 DHW Profile (S3)" )
> TLShape = ( "EL1 TskLtg Profile (S1)", "EL1 TskLtg Profile (S2)",
> "EL1 TskLtg Profile (S3)" )
> TLElecIntens[1] = 0.02
> SCRShape = ( "EL1 S-C Refrig Profile (S1)",
> "EL1 S-C Refrig Profile (S2)",
> "EL1 S-C Refrig Profile (S3)" )
> DaylitAreaCurrent[3] = 1
> HasPitchedRoof = 0
> RoofZoneErrorCode = 4
> RoofEndIsGable[28] = 0
> RoofEndIsGable[36] = 0
> BDBaseUpdateFlag[3] = 0
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S1)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jan)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Feb)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Mar)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Apr)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (May)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jun)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jul)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Aug)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Sep)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Oct)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Nov)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Dec)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S1)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S1)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S1)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S1)"
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S2)"
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S3)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S2)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S3)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S1)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S2)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S3)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jan)"
> ..
>
> DayShape "EL1 Refrig DayShape (Feb)"
> ..
>
> DayShape "EL1 Refrig DayShape (Mar)"
> ..
>
> DayShape "EL1 Refrig DayShape (Apr)"
> ..
>
> DayShape "EL1 Refrig DayShape (May)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jun)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jul)"
> ..
>
> DayShape "EL1 Refrig DayShape (Aug)"
> ..
>
> DayShape "EL1 Refrig DayShape (Sep)"
> ..
>
> DayShape "EL1 Refrig DayShape (Oct)"
> ..
>
> DayShape "EL1 Refrig DayShape (Nov)"
> ..
>
> DayShape "EL1 Refrig DayShape (Dec)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S2)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S3)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S2)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S3)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S2)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S3)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S1)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S2)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S3)"
> ..
>
> ZnGrpWiz "EL1 Ground Floor"
> ShortName = "GndFlr"
> ..
>
> CustomZone "Custom Zone 1"
> NumVerts = 8
> X[1] = 6.85
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 40.35
> X[5] = 32.5
> X[6] = 16.3
> X[7] = 18.5
> X[8] = 18.5
> Y[1] = 35.45
> Y[2] = 35.45
> Y[3] = 56.45
> Y[4] = 56.65
> Y[5] = 56.65
> Y[6] = 56.65
> Y[7] = 52.5
> Y[8] = 40.35
> ..
>
> CustomZone "Custom Zone 2"
> NumVerts = 4
> X[1] = 6.85
> X[2] = 6.85
> X[3] = 16.3
> X[4] = 17.5
> Y[1] = 67.95
> Y[2] = 56.75
> Y[3] = 56.65
> Y[4] = 67.95
> ..
>
> CustomZone "Custom Zone 3"
> NumVerts = 5
> X[1] = 17.5
> X[2] = 16.3
> X[3] = 32.5
> X[4] = 33.35
> X[5] = 27.05
> Y[1] = 67.95
> Y[2] = 56.65
> Y[3] = 56.65
> Y[4] = 67.5
> Y[5] = 67.45
> ..
>
> CustomZone "Custom Zone 4"
> NumVerts = 4
> X[1] = 32.5
> X[2] = 40.35
> X[3] = 41
> X[4] = 33.35
> Y[1] = 56.65
> Y[2] = 56.65
> Y[3] = 67.5
> Y[4] = 67.5
> ..
>
> CustomZone "Custom Zone 5"
> NumVerts = 4
> X[1] = 41
> X[2] = 40.35
> X[3] = 46.5
> X[4] = 46.5
> Y[1] = 67.5
> Y[2] = 56.65
> Y[3] = 56.45
> Y[4] = 67.45
> ..
>
> CustomZone "Custom Zone 6"
> NumVerts = 10
> X[1] = 46.5
> X[2] = 46.5
> X[3] = 27.9
> X[4] = 27.85
> X[5] = 27.85
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.05
> X[9] = 33.35
> X[10] = 41
> Y[1] = 67.45
> Y[2] = 92.8
> Y[3] = 92.75
> Y[4] = 88.1
> Y[5] = 81.7
> Y[6] = 78.1
> Y[7] = 71.8
> Y[8] = 67.45
> Y[9] = 67.5
> Y[10] = 67.5
> ..
>
> CustomZone "Custom Zone 7"
> NumVerts = 8
> X[1] = 27.9
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 25.85
> X[5] = 27.85
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> Y[1] = 92.75
> Y[2] = 92.8
> Y[3] = 117.8
> Y[4] = 118.15
> Y[5] = 113.45
> Y[6] = 107.2
> Y[7] = 103.45
> Y[8] = 97.2
> ..
>
> CustomZone "Custom Zone 8"
> NumVerts = 5
> X[1] = 25.85
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 25.65
> X[5] = 25.5
> Y[1] = 118.15
> Y[2] = 117.8
> Y[3] = 129.3
> Y[4] = 129.15
> Y[5] = 123.45
> ..
>
> CustomZone "Custom Zone 9"
> NumVerts = 4
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.4
> X[4] = 25.5
> Y[1] = 129.15
> Y[2] = 129.1
> Y[3] = 123.5
> Y[4] = 123.45
> ..
>
> CustomZone "Custom Zone 10"
> NumVerts = 4
> X[1] = 17.4
> X[2] = 17.45
> X[3] = 25.85
> X[4] = 25.5
> Y[1] = 123.5
> Y[2] = 118.2
> Y[3] = 118.15
> Y[4] = 123.45
> ..
>
> CustomZone "Custom Zone 11"
> NumVerts = 9
> X[1] = 25.65
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 42.65
> X[5] = 27.9
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 27.85
> Y[1] = 129.15
> Y[2] = 129.3
> Y[3] = 155.15
> Y[4] = 155.15
> Y[5] = 154.1
> Y[6] = 149.6
> Y[7] = 143.5
> Y[8] = 139.7
> Y[9] = 133.5
> ..
>
> CustomZone "Custom Zone 12"
> NumVerts = 5
> X[1] = 42.6
> X[2] = 18
> X[3] = 17.45
> X[4] = 27.9
> X[5] = 42.65
> Y[1] = 164.5
> Y[2] = 164.5
> Y[3] = 153.65
> Y[4] = 154.1
> Y[5] = 155.15
> ..
>
> CustomZone "Custom Zone 13"
> NumVerts = 4
> X[1] = 18
> X[2] = 42.6
> X[3] = 42.7
> X[4] = 18
> Y[1] = 164.5
> Y[2] = 164.5
> Y[3] = 167.05
> Y[4] = 166.5
> ZoneType = "Unconditioned"
> ..
>
> CustomZone "Custom Zone 14"
> NumVerts = 5
> X[1] = 42.7
> X[2] = 42.65
> X[3] = 27.05
> X[4] = 17.5
> X[5] = 18
> Y[1] = 167.05
> Y[2] = 175.85
> Y[3] = 176.85
> Y[4] = 177.4
> Y[5] = 166.5
> ..
>
> CustomZone "Custom Zone 15"
> NumVerts = 4
> X[1] = 13.5
> X[2] = 13.1
> X[3] = 6.8
> X[4] = 6.8
> Y[1] = 169.9
> Y[2] = 177.4
> Y[3] = 177.4
> Y[4] = 170.45
> ZoneType = "Conditioned"
> ..
>
> CustomZone "Custom Zone 16"
> NumVerts = 8
> X[1] = 17.5
> X[2] = 13.1
> X[3] = 13.5
> X[4] = 6.8
> X[5] = 6.8
> X[6] = 17.45
> X[7] = 18
> X[8] = 18
> Y[1] = 177.4
> Y[2] = 177.4
> Y[3] = 169.9
> Y[4] = 170.45
> Y[5] = 153.65
> Y[6] = 153.65
> Y[7] = 164.5
> Y[8] = 166.5
> ..
>
> CustomZone "Custom Zone 17"
> NumVerts = 9
> X[1] = 27.05
> X[2] = 42.65
> X[3] = 46.5
> X[4] = 46.5
> X[5] = 25.65
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 27.85
> Y[1] = 176.85
> Y[2] = 175.85
> Y[3] = 175.9
> Y[4] = 201.9
> Y[5] = 201.9
> Y[6] = 197.5
> Y[7] = 191.25
> Y[8] = 187.55
> Y[9] = 181.25
> ..
>
> CustomZone "Custom Zone 18"
> NumVerts = 5
> X[1] = 46.5
> X[2] = 46.5
> X[3] = 25.65
> X[4] = 25.15
> X[5] = 25.65
> Y[1] = 201.9
> Y[2] = 213.2
> Y[3] = 213.2
> Y[4] = 207.4
> Y[5] = 201.9
> ..
>
> CustomZone "Custom Zone 19"
> NumVerts = 4
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.4
> X[4] = 25.15
> Y[1] = 213.2
> Y[2] = 213.2
> Y[3] = 207.75
> Y[4] = 207.4
> ..
>
> CustomZone "Custom Zone 20"
> NumVerts = 4
> X[1] = 25.15
> X[2] = 17.4
> X[3] = 17.45
> X[4] = 25.65
> Y[1] = 207.4
> Y[2] = 207.75
> Y[3] = 201.8
> Y[4] = 201.9
> ..
>
> CustomZone "Custom Zone 21"
> NumVerts = 9
> X[1] = 25.65
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 43.4
> X[5] = 27.85
> X[6] = 27.65
> X[7] = 27.65
> X[8] = 27.7
> X[9] = 27.7
> Y[1] = 213.2
> Y[2] = 213.2
> Y[3] = 236.1
> Y[4] = 238.55
> Y[5] = 238.5
> Y[6] = 233.8
> Y[7] = 227.55
> Y[8] = 223.75
> Y[9] = 217.5
> ..
>
> CustomZone "Custom Zone 22"
> NumVerts = 14
> X[1] = 27.65
> X[2] = 27.85
> X[3] = 43.4
> X[4] = 46.5
> X[5] = 55.55
> X[6] = 58.5
> X[7] = 45.5
> X[8] = 46
> X[9] = 46.5
> X[10] = 46.5
> X[11] = 17.5
> X[12] = 27.4
> X[13] = 27.4
> X[14] = 27.65
> Y[1] = 245.8
> Y[2] = 238.5
> Y[3] = 238.55
> Y[4] = 236.1
> Y[5] = 232.15
> Y[6] = 238.5
> Y[7] = 244.2
> Y[8] = 254.9
> Y[9] = 267.75
> Y[10] = 273.55
> Y[11] = 273.55
> Y[12] = 265.3
> Y[13] = 259.05
> Y[14] = 252.05
> ..
>
> CustomZone "Custom Zone 23"
> NumVerts = 5
> X[1] = 46.5
> X[2] = 46
> X[3] = 57.2
> X[4] = 59.3
> X[5] = 61.45
> Y[1] = 267.75
> Y[2] = 254.9
> Y[3] = 250.55
> Y[4] = 255.45
> Y[5] = 261.25
> ..
>
> CustomZone "Custom Zone 24"
> NumVerts = 5
> X[1] = 46
> X[2] = 45.5
> X[3] = 58.5
> X[4] = 62.5
> X[5] = 57.2
> Y[1] = 254.9
> Y[2] = 244.2
> Y[3] = 238.5
> Y[4] = 247.7
> Y[5] = 250.55
> ..
>
> CustomZone "Custom Zone 25"
> NumVerts = 4
> X[1] = 67.55
> X[2] = 61.45
> X[3] = 59.3
> X[4] = 65.1
> Y[1] = 258.5
> Y[2] = 261.25
> Y[3] = 255.45
> Y[4] = 252.7
> ..
>
> CustomZone "Custom Zone 26"
> NumVerts = 4
> X[1] = 59.3
> X[2] = 57.2
> X[3] = 62.5
> X[4] = 65.1
> Y[1] = 255.45
> Y[2] = 250.55
> Y[3] = 247.7
> Y[4] = 252.7
> ..
>
> CustomZone "Custom Zone 27"
> NumVerts = 10
> X[1] = 55.55
> X[2] = 78.9
> X[3] = 87.25
> X[4] = 82.45
> X[5] = 76.45
> X[6] = 73.35
> X[7] = 67.55
> X[8] = 65.1
> X[9] = 62.5
> X[10] = 58.5
> Y[1] = 232.15
> Y[2] = 222
> Y[3] = 241.05
> Y[4] = 241
> Y[5] = 243.4
> Y[6] = 244.9
> Y[7] = 247.5
> Y[8] = 252.7
> Y[9] = 247.7
> Y[10] = 238.5
> ..
>
> CustomZone "Custom Zone 28"
> NumVerts = 4
> X[1] = 90.5
> X[2] = 87.25
> X[3] = 92.8
> X[4] = 95.65
> Y[1] = 248.55
> Y[2] = 241.05
> Y[3] = 239.2
> Y[4] = 246.3
> ..
>
> CustomZone "Custom Zone 29"
> NumVerts = 5
> X[1] = 78.9
> X[2] = 89.3
> X[3] = 97.55
> X[4] = 92.8
> X[5] = 87.25
> Y[1] = 222
> Y[2] = 217.45
> Y[3] = 236.4
> Y[4] = 239.2
> Y[5] = 241.05
> ..
>
> CustomZone "Custom Zone 30"
> NumVerts = 4
> X[1] = 92.8
> X[2] = 97.55
> X[3] = 100.35
> X[4] = 95.65
> Y[1] = 239.2
> Y[2] = 236.4
> Y[3] = 244.3
> Y[4] = 246.3
> ..
>
> CustomZone "Custom Zone 31"
> NumVerts = 10
> X[1] = 100.85
> X[2] = 97.55
> X[3] = 89.3
> X[4] = 113.15
> X[5] = 114.65
> X[6] = 118
> X[7] = 119.7
> X[8] = 115.85
> X[9] = 109.75
> X[10] = 106.45
> Y[1] = 233
> Y[2] = 236.4
> Y[3] = 217.45
> Y[4] = 207.05
> Y[5] = 210.55
> Y[6] = 219.45
> Y[7] = 224.5
> Y[8] = 226.25
> Y[9] = 228.9
> Y[10] = 230.3
> MultiLevel = 0
> ..
>
> CustomZone "Custom Zone 32"
> NumVerts = 5
> X[1] = 123.8
> X[2] = 119.7
> X[3] = 118
> X[4] = 127.4
> X[5] = 133.2
> Y[1] = 234.05
> Y[2] = 224.5
> Y[3] = 219.45
> Y[4] = 215.35
> Y[5] = 229.95
> ..
>
> CustomZone "Custom Zone 33"
> NumVerts = 4
> X[1] = 118
> X[2] = 114.65
> X[3] = 123.1
> X[4] = 127.4
> Y[1] = 219.45
> Y[2] = 210.55
> Y[3] = 206.85
> Y[4] = 215.35
> ..
>
> CustomZone "Custom Zone 34"
> NumVerts = 9
> X[1] = 121.6
> X[2] = 145.9
> X[3] = 161.75
> X[4] = 153.45
> X[5] = 150.5
> X[6] = 139.6
> X[7] = 133.2
> X[8] = 127.4
> X[9] = 123.1
> Y[1] = 203.35
> Y[2] = 192.75
> Y[3] = 229.1
> Y[4] = 228
> Y[5] = 221.3
> Y[6] = 225.9
> Y[7] = 229.95
> Y[8] = 215.35
> Y[9] = 206.85
> ..
>
> CustomZone "Custom Zone 35"
> NumVerts = 4
> X[1] = 10.65
> X[2] = 10.65
> X[3] = 18.5
> X[4] = 18.5
> Y[1] = 52.5
> Y[2] = 40.35
> Y[3] = 40.35
> Y[4] = 52.5
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 36"
> NumVerts = 4
> X[1] = 27.85
> X[2] = 19.2
> X[3] = 19.2
> X[4] = 27.85
> Y[1] = 88.1
> Y[2] = 88.1
> Y[3] = 81.7
> Y[4] = 81.7
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 37"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 71.85
> Y[2] = 71.8
> Y[3] = 78.1
> Y[4] = 78.1
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 38"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 97.2
> Y[2] = 97.2
> Y[3] = 103.45
> Y[4] = 103.45
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 39"
> NumVerts = 4
> X[1] = 27.85
> X[2] = 27.85
> X[3] = 19.2
> X[4] = 19.2
> Y[1] = 107.2
> Y[2] = 113.45
> Y[3] = 113.45
> Y[4] = 107.2
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 40"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 19.2
> X[3] = 27.85
> X[4] = 27.85
> Y[1] = 149.75
> Y[2] = 143.5
> Y[3] = 143.5
> Y[4] = 149.6
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 41"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 133.5
> Y[2] = 133.5
> Y[3] = 139.7
> Y[4] = 139.7
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 42"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19
> Y[1] = 181.25
> Y[2] = 181.25
> Y[3] = 187.55
> Y[4] = 187.55
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 43"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19
> Y[1] = 191.25
> Y[2] = 191.25
> Y[3] = 197.5
> Y[4] = 197.5
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 44"
> NumVerts = 4
> X[1] = 19
> X[2] = 19
> X[3] = 27.65
> X[4] = 27.65
> Y[1] = 233.8
> Y[2] = 227.55
> Y[3] = 227.55
> Y[4] = 233.8
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 45"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.65
> X[3] = 27.65
> X[4] = 19
> Y[1] = 245.8
> Y[2] = 245.8
> Y[3] = 252.05
> Y[4] = 252.05
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 46"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.4
> X[3] = 27.4
> X[4] = 19
> Y[1] = 259.05
> Y[2] = 259.05
> Y[3] = 265.3
> Y[4] = 265.3
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 47"
> NumVerts = 4
> X[1] = 71
> X[2] = 67.55
> X[3] = 73.35
> X[4] = 76.8
> Y[1] = 255.4
> Y[2] = 247.5
> Y[3] = 244.9
> Y[4] = 252.8
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 48"
> NumVerts = 4
> X[1] = 76.45
> X[2] = 82.45
> X[3] = 85.9
> X[4] = 80.15
> Y[1] = 243.4
> Y[2] = 241
> Y[3] = 248.95
> Y[4] = 251.45
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 49"
> NumVerts = 4
> X[1] = 104.3
> X[2] = 100.85
> X[3] = 106.45
> X[4] = 110.05
> Y[1] = 240.75
> Y[2] = 233
> Y[3] = 230.3
> Y[4] = 238.4
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 50"
> NumVerts = 4
> X[1] = 109.75
> X[2] = 115.85
> X[3] = 119.2
> X[4] = 113.45
> Y[1] = 228.9
> Y[2] = 226.25
> Y[3] = 234.4
> Y[4] = 236.9
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 51"
> NumVerts = 4
> X[1] = 142.9
> X[2] = 139.6
> X[3] = 150.5
> X[4] = 153.45
> Y[1] = 232.6
> Y[2] = 225.9
> Y[3] = 221.3
> Y[4] = 228
> MultiLevel = 1
> ..
>
> ZnGrpWiz "Exhausted Zone Group 2"
> ShortName = "GndFlr"
> HaveExhaustFans = 1
> XFanFlow = 660
> XFanMotorEff = "High"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S1)"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S2)"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S3)"
> ..
>
> CustomZone "Custom Zone 52"
> NumVerts = 4
> X[1] = 19.05
> X[2] = 27.7
> X[3] = 27.7
> X[4] = 19
> Y[1] = 217.5
> Y[2] = 217.5
> Y[3] = 223.75
> Y[4] = 223.75
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 53"
> NumVerts = 12
> X[1] = 27.85
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 25.65
> X[5] = 27.7
> X[6] = 19.05
> X[7] = 19
> X[8] = 27.7
> X[9] = 27.65
> X[10] = 19
> X[11] = 19
> X[12] = 27.65
> Y[1] = 238.5
> Y[2] = 238.2
> Y[3] = 213.2
> Y[4] = 213.2
> Y[5] = 217.5
> Y[6] = 217.5
> Y[7] = 223.75
> Y[8] = 223.75
> Y[9] = 227.55
> Y[10] = 227.55
> Y[11] = 233.8
> Y[12] = 233.8
> ..
>
> CustomZone "Custom Zone 54"
> NumVerts = 12
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.5
> X[4] = 27.05
> X[5] = 27.85
> X[6] = 19
> X[7] = 19
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19
> X[11] = 19
> X[12] = 27.85
> Y[1] = 201.9
> Y[2] = 201.8
> Y[3] = 177.4
> Y[4] = 176.85
> Y[5] = 181.25
> Y[6] = 181.25
> Y[7] = 187.55
> Y[8] = 187.55
> Y[9] = 191.25
> Y[10] = 191.25
> Y[11] = 197.5
> Y[12] = 197.5
> ..
>
> CustomZone "Custom Zone 55"
> NumVerts = 12
> X[1] = 27.9
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 25.65
> X[5] = 27.85
> X[6] = 19.2
> X[7] = 19.2
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19.2
> X[11] = 19.2
> X[12] = 27.85
> Y[1] = 154.1
> Y[2] = 153.65
> Y[3] = 129.1
> Y[4] = 129.15
> Y[5] = 133.5
> Y[6] = 133.5
> Y[7] = 139.7
> Y[8] = 139.7
> Y[9] = 143.5
> Y[10] = 143.5
> Y[11] = 149.75
> Y[12] = 149.6
> ..
>
> CustomZone "Custom Zone 56"
> NumVerts = 12
> X[1] = 25.85
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 27.9
> X[5] = 27.85
> X[6] = 19.2
> X[7] = 19.2
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19.2
> X[11] = 19.2
> X[12] = 27.85
> Y[1] = 118.15
> Y[2] = 118.2
> Y[3] = 92.8
> Y[4] = 92.75
> Y[5] = 97.2
> Y[6] = 97.2
> Y[7] = 103.45
> Y[8] = 103.45
> Y[9] = 107.2
> Y[10] = 107.2
> Y[11] = 113.45
> Y[12] = 113.45
> ..
>
> CustomZone "Custom Zone 57"
> NumVerts = 12
> X[1] = 17.45
> X[2] = 17.5
> X[3] = 27.05
> X[4] = 27.85
> X[5] = 19.2
> X[6] = 19.2
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 19.2
> X[10] = 19.2
> X[11] = 27.85
> X[12] = 27.9
> Y[1] = 92.8
> Y[2] = 67.95
> Y[3] = 67.45
> Y[4] = 71.8
> Y[5] = 71.85
> Y[6] = 78.1
> Y[7] = 78.1
> Y[8] = 81.7
> Y[9] = 81.7
> Y[10] = 88.1
> Y[11] = 88.1
> Y[12] = 92.75
> ..
>
> CustomZone "Custom Zone 58"
> NumVerts = 7
> X[1] = 16.3
> X[2] = 6.85
> X[3] = 6.85
> X[4] = 18.5
> X[5] = 10.65
> X[6] = 10.65
> X[7] = 18.5
> Y[1] = 56.65
> Y[2] = 56.75
> Y[3] = 35.45
> Y[4] = 40.35
> Y[5] = 40.35
> Y[6] = 52.5
> Y[7] = 52.5
> ..
>
> CustomZone "Custom Zone 59"
> NumVerts = 11
> X[1] = 17.5
> X[2] = 17.45
> X[3] = 27.85
> X[4] = 27.65
> X[5] = 19
> X[6] = 19
> X[7] = 27.65
> X[8] = 27.4
> X[9] = 19
> X[10] = 19
> X[11] = 27.4
> Y[1] = 273.55
> Y[2] = 238.2
> Y[3] = 238.5
> Y[4] = 245.8
> Y[5] = 245.8
> Y[6] = 252.05
> Y[7] = 252.05
> Y[8] = 259.05
> Y[9] = 259.05
> Y[10] = 265.3
> Y[11] = 265.3
> ..
>
> CustomZone "Custom Zone 60"
> NumVerts = 12
> X[1] = 67.55
> X[2] = 65.1
> X[3] = 67.55
> X[4] = 71
> X[5] = 76.8
> X[6] = 73.35
> X[7] = 76.45
> X[8] = 80.15
> X[9] = 85.9
> X[10] = 82.45
> X[11] = 87.25
> X[12] = 90.5
> Y[1] = 258.5
> Y[2] = 252.7
> Y[3] = 247.5
> Y[4] = 255.4
> Y[5] = 252.8
> Y[6] = 244.9
> Y[7] = 243.4
> Y[8] = 251.45
> Y[9] = 248.95
> Y[10] = 241
> Y[11] = 241.05
> Y[12] = 248.55
> ..
>
> CustomZone "Custom Zone 61"
> NumVerts = 12
> X[1] = 100.35
> X[2] = 97.55
> X[3] = 100.85
> X[4] = 104.3
> X[5] = 110.05
> X[6] = 106.45
> X[7] = 109.75
> X[8] = 113.45
> X[9] = 119.2
> X[10] = 115.85
> X[11] = 119.7
> X[12] = 123.8
> Y[1] = 244.3
> Y[2] = 236.4
> Y[3] = 233
> Y[4] = 240.75
> Y[5] = 238.4
> Y[6] = 230.3
> Y[7] = 228.9
> Y[8] = 236.9
> Y[9] = 234.4
> Y[10] = 226.25
> Y[11] = 224.5
> Y[12] = 234.05
> ..
>
> CustomZone "Custom Zone 62"
> NumVerts = 6
> X[1] = 161.75
> X[2] = 137.45
> X[3] = 133.2
> X[4] = 139.6
> X[5] = 142.9
> X[6] = 153.45
> Y[1] = 229.1
> Y[2] = 239.7
> Y[3] = 229.95
> Y[4] = 225.9
> Y[5] = 232.6
> Y[6] = 228
> ..
>
> ZnGrpWiz "ERV Zone Group 3"
> ShortName = "GndFlr"
> AssignedSystem = "ERV"
> ..
>
> ZnGrpWiz "Unconditioned Zone Group 4"
> ShortName = "GndFlr"
> IsConditioned = 0
> ..
>
> DiagData "Bldg Envelope & Loads 1 Diag Data"
> PolyWndShowGrid = 0
> PolyWndGridRes = 2
> PolyWndDWGSnapRad = 0.25
> PolyWndPlySnapRad = 0.25
> PolyWndLwrLeftX = -149.2
> PolyWndLwrLeftY = 9.45
> PolyWndWidth = 466.333
> PolyWndSnapOrder = ( 2, 1, 0 )
> ShowCADLayer[1] = 1
> ShowCADLayer[2] = 0
> ShowCADLayer[3] = 0
> ShowCADLayer[4] = 1
> ShowCADLayer[5] = 1
> ShowCADLayer[6] = 1
> ShowCADLayer[7] = 1
> ShowCADLayer[8] = 1
> ShowCADLayer[9] = 1
> ShowCADLayer[10] = 1
> ShowCADLayer[11] = 1
> ShowCADLayer[12] = 1
> ShowCADLayer[13] = 1
> ShowCADLayer[14] = 1
> ShowCADLayer[15] = 1
> ShowCADLayer[16] = 1
> ShowCADLayer[17] = 1
> ShowCADLayer[18] = 1
> ShowCADLayer[19] = 1
> ShowCADLayer[20] = 1
> ShowCADLayer[21] = 1
> ShowCADLayer[22] = 1
> ShowCADLayer[23] = 1
> ShowCADLayer[24] = 1
> ShowCADLayer[25] = 1
> ShowCADLayer[26] = 1
> ShowCADLayer[27] = 1
> ShowCADLayer[28] = 1
> ShowCADLayer[29] = 1
> ShowCADLayer[30] = 1
> ShowCADLayer[31] = 1
> ShowCADLayer[32] = 1
> ShowCADLayer[33] = 1
> ShowCADLayer[34] = 1
> ShowCADLayer[35] = 1
> ShowCADLayer[36] = 1
> ShowCADLayer[37] = 0
> ShowCADLayer[38] = 1
> ShowCADLayer[39] = 1
> ShowCADLayer[40] = 1
> ShowCADLayer[41] = 1
> ShowCADLayer[42] = 1
> ShowCADLayer[43] = 1
> ShowCADLayer[44] = 1
> ShowCADLayer[45] = 1
> ShowCADLayer[46] = 1
> ShowCADLayer[47] = 1
> ShowCADLayer[48] = 1
> ShowCADLayer[49] = 1
> ShowCADLayer[50] = 1
> ShowCADLayer[51] = 1
> ShowCADLayer[52] = 1
> ShowCADLayer[53] = 1
> ShowCADLayer[54] = 1
> ShowCADLayer[55] = 1
> ShowCADLayer[56] = 1
> ShowCADLayer[57] = 1
> ShowCADLayer[58] = 1
> ShowCADLayer[59] = 1
> ShowCADLayer[60] = 1
> ShowCADLayer[61] = 0
> ShowCADLayer[62] = 1
> ShowCADLayer[63] = 1
> ShowCADLayer[64] = 1
> ShowCADLayer[65] = 1
> ShowCADLayer[66] = 1
> ShowCADLayer[67] = 1
> ShowCADLayer[68] = 1
> ShowCADLayer[69] = 1
> ShowCADLayer[70] = 1
> ShowCADLayer[71] = 1
> ShowCADLayer[72] = 0
> ShowCADLayer[73] = 1
> ShowCADLayer[74] = 1
> ShowCADLayer[75] = 1
> ShowCADLayer[76] = 1
> ShowCADLayer[77] = 1
> ShowCADLayer[78] = 1
> ShowCADLayer[79] = 1
> ShowCADLayer[80] = 1
> ShowCADLayer[81] = 1
> ShowCADLayer[82] = 1
> ShowCADLayer[83] = 1
> CADFileComp = "3022.AS10_rcp - DWG"
> ..
>
> CADFile "3022.AS10_base - DWG"
> FileName = "DWGs\3022.AS10_base.dwg"
> FilePathOffset = 3
> ScaleUnits = 0
> ScaleValue = 1
> OriginX = -431.854
> OriginY = -202.058
> Azimuth = 0
> ..
>
> CADFile "3022.AS10_rcp - DWG"
> FileName = "DWGs\3022.AS10_rcp.dwg"
> FilePathOffset = 3
> ScaleUnits = 0
> ScaleValue = 1
> OriginX = -432.278
> OriginY = -201.587
> Azimuth = 0
> ..
>
> HVACWiz "HVAC System 1"
> ScreenIDArrIdx = 0
> OldFurnAFUEDflt = ( 1, 1 )
> SystemPerWhat[1] = "System per Shell"
> ..
>
> HVACWiz "ERV"
> ScreenIDArrIdx = 1
> ScreenIDArrID = 121
> CoolSource[1] = "No Cooling"
> HVACSysType[1] = "Unit Ventilator (no heating or cooling)"
> OldFurnAFUEDflt = ( 1, 1 )
> ..
>
> DXCWWiz "Water-Cooled DX System"
> ..
>
> WSECWWiz "Wtr-Side Econo System"
> ..
>
> WLHPWiz "WLHP System"
> ..
>
> GSHPWiz "GSHP System"
> ..
>
> PrimWiz "Primary HVAC Plant"
> ..
>
> DHWWiz "DHW Plant"
> ..
>
> FacetColor "By Wall Type"
> FacetType = "Walls"
> ColorOption = "By Wall Type"
> ..
>
> FacetColor "By Construction"
> FacetType = "Walls"
> ColorOption = "By Construction"
> ..
>
> FacetColor "Uniform"
> FacetType = "Windows"
> ColorOption = "Uniform"
> ..
>
> FacetColor "By Glass Type"
> FacetType = "Windows"
> ColorOption = "By Glass Type"
> ..
>
> Light3D "Light3D - Default"
> Type = "Default"
> ..
>
> Light3D "Light3D - User1"
> Type = "User Defined 1"
> ..
>
> Light3D "Light3D - User2"
> Type = "User Defined 2"
> ..
>
> Light3D "Light3D - User3"
> Type = "User Defined 3"
> ..
>
> Light3D "Light3D - User4"
> Type = "User Defined 4"
> ..
>
> Light3D "Light3D - User5"
> Type = "User Defined 5"
> ..
>
>
> END_OF_FILE
>
> Proj "0849-APS Phase II 12-10-08 erv"
> ProgramVersion = "eQUEST 3.62.6236"
> BDBaseVersion = 22
> ProductCode = "eQUEST"
> WeatherFile = "TMY2\ALBUQUNM.bin"
> CreateDate = 1228503283
> ModDate = 1232232168
> RunDate = 1232232047
> LibraryFile = "eQ_Lib.dat"
> ActiveMode = 0
> InputModule = 4
> UseCameraData = 1
> ClippingRange = ( 131.756, 454.319 )
> FocalPoint = ( 84.0581, 154.325, 10.2624 )
> Position = ( -79.2852, -62.439, 49.6857 )
> ViewUpVector = ( 0, 0, 1 )
> ViewAngle = 25.3151
> InterfaceMode = 1
> AllowWizard = 1
> NotProjFile = "0849-APS Phase II 12-10-08 erv"
> InputUnitsType = "English"
> OutputUnitsType = "English"
> PreviousName = "0849-APS Phase II 12-10-08 proposed"
> DetailedModelEdits = 1
> ProjTreeType[2] = 1
> ProjTreeType[3] = 1
> ProjTreeType[4] = 1
> ProjTreeType[5] = 1
> ProjTreeID[2] = 10080000
> ProjTreeID[3] = 10080062
> ProjTreeID[4] = 10820000
> ProjTreeID[5] = 10480003
> ProjTreeLabel[2] = "Common LTWL ML Spc (ML.C1)"
> ProjTreeLabel[3] = "EL1 SSE Perim Plnm (G.SSE63)"
> ProjTreeLabel[4] = "GLHX (VertWell-CM)"
> ProjTreeLabel[5] = "WLHP 208"
> BDBUpdateReEval = 0
> ..
>
> MainWiz "0849-APS Phase II 12-10-08 erv"
> ProductCode = "eQUEST"
> WizardType = "Design Development"
> DebugID = 0
> AllowCustWinDoor = 1
> ScreenIDArrIdx = 6
> ScreenIDArrID = 250
> Coverage = "All eQUEST Locations"
> State = "New Mexico"
> Location = "Albuquerque"
> BldgType = "School, K-6 Elementary"
> ..
>
> ShellWiz "Phase II"
> ModelEnduse[3] = 0
> ModelEnduse[4] = 0
> ModelEnduse[5] = 0
> ModelEnduse[12] = 0
> ModelEnduse[13] = 1
> ScreenIDArrIdx = 1
> ScreenIDArrID = 22
> BldgType = "School, K-6 Elementary"
> GrossArea = 11008
> Footprint = "- custom -"
> FlrToFlr = 12.5
> ZoningPattern = "- custom -"
> NumMCZnGrps = 0
> DiagLink = "Bldg Envelope & Loads 1 Diag Data"
> RoofInsulLocation = "Roof Surface"
> CeilingConsType = "Lay-In Acoustic Tile"
> GrndFlrConsType = "4 in. Concrete"
> GrndFlrInsType = "vert ext bd, R-5, 2ft deep"
> GrndFlrSecInsType = "Vinyl Tile"
> ZoningCurrent = 1
> NumFloorVertices = 53
> FloorVertX[1] = 6.85
> FloorVertX[2] = 46.5
> FloorVertX[3] = 46.5
> FloorVertX[4] = 46.5
> FloorVertX[5] = 46.5
> FloorVertX[6] = 46.5
> FloorVertX[7] = 46.5
> FloorVertX[8] = 46.5
> FloorVertX[9] = 42.65
> FloorVertX[10] = 42.6
> FloorVertX[11] = 42.7
> FloorVertX[12] = 42.65
> FloorVertX[13] = 46.5
> FloorVertX[14] = 46.5
> FloorVertX[15] = 46.5
> FloorVertX[16] = 46.5
> FloorVertX[17] = 55.55
> FloorVertX[18] = 78.9
> FloorVertX[19] = 89.3
> FloorVertX[20] = 113.15
> FloorVertX[21] = 114.65
> FloorVertX[22] = 123.1
> FloorVertX[23] = 121.6
> FloorVertX[24] = 145.9
> FloorVertX[25] = 161.75
> FloorVertX[26] = 137.45
> FloorVertX[27] = 133.2
> FloorVertX[28] = 123.8
> FloorVertX[29] = 100.35
> FloorVertX[30] = 95.65
> FloorVertX[31] = 90.5
> FloorVertX[32] = 67.55
> FloorVertX[33] = 61.45
> FloorVertX[34] = 46.5
> FloorVertX[35] = 46.5
> FloorVertX[36] = 17.5
> FloorVertX[37] = 17.45
> FloorVertX[38] = 17.45
> FloorVertX[39] = 17.4
> FloorVertX[40] = 17.45
> FloorVertX[41] = 17.5
> FloorVertX[42] = 13.1
> FloorVertX[43] = 6.8
> FloorVertX[44] = 6.8
> FloorVertX[45] = 6.8
> FloorVertX[46] = 17.45
> FloorVertX[47] = 17.45
> FloorVertX[48] = 17.4
> FloorVertX[49] = 17.45
> FloorVertX[50] = 17.45
> FloorVertX[51] = 17.5
> FloorVertX[52] = 6.85
> FloorVertX[53] = 6.85
> FloorVertY[1] = 35.45
> FloorVertY[2] = 35.45
> FloorVertY[3] = 56.45
> FloorVertY[4] = 67.45
> FloorVertY[5] = 92.8
> FloorVertY[6] = 117.8
> FloorVertY[7] = 129.3
> FloorVertY[8] = 155.15
> FloorVertY[9] = 155.15
> FloorVertY[10] = 164.5
> FloorVertY[11] = 167.05
> FloorVertY[12] = 175.85
> FloorVertY[13] = 175.9
> FloorVertY[14] = 201.9
> FloorVertY[15] = 213.2
> FloorVertY[16] = 236.1
> FloorVertY[17] = 232.15
> FloorVertY[18] = 222
> FloorVertY[19] = 217.45
> FloorVertY[20] = 207.05
> FloorVertY[21] = 210.55
> FloorVertY[22] = 206.85
> FloorVertY[23] = 203.35
> FloorVertY[24] = 192.75
> FloorVertY[25] = 229.1
> FloorVertY[26] = 239.7
> FloorVertY[27] = 229.95
> FloorVertY[28] = 234.05
> FloorVertY[29] = 244.3
> FloorVertY[30] = 246.3
> FloorVertY[31] = 248.55
> FloorVertY[32] = 258.5
> FloorVertY[33] = 261.25
> FloorVertY[34] = 267.75
> FloorVertY[35] = 273.55
> FloorVertY[36] = 273.55
> FloorVertY[37] = 238.2
> FloorVertY[38] = 213.2
> FloorVertY[39] = 207.75
> FloorVertY[40] = 201.8
> FloorVertY[41] = 177.4
> FloorVertY[42] = 177.4
> FloorVertY[43] = 177.4
> FloorVertY[44] = 170.45
> FloorVertY[45] = 153.65
> FloorVertY[46] = 153.65
> FloorVertY[47] = 129.1
> FloorVertY[48] = 123.5
> FloorVertY[49] = 118.2
> FloorVertY[50] = 92.8
> FloorVertY[51] = 67.95
> FloorVertY[52] = 67.95
> FloorVertY[53] = 56.75
> AdiabaticCurrent = 1
> GroundZnGrp[4] = "Exhausted Zone Group 2"
> GroundZnGrp[12] = "Exhausted Zone Group 2"
> GroundZnGrp[13] = "Unconditioned Zone Group 4"
> GroundZnGrp[14] = "Exhausted Zone Group 2"
> GroundZnGrp[16] = "ERV Zone Group 3"
> GroundZnGrp[25] = "EL1 Ground Floor"
> GroundZnGrp[32] = "ERV Zone Group 3"
> ZoneGroupsOK = 1
> DfltZnGrpName = ( "EL1 Underground Areas", "EL1 Ground Floor",
> "EL1 Ground Floor", "EL1 Typical Floor(s)",
> "EL1 Typical Floor(s)", "EL1 Top Floor",
> "EL1 Top Floor" )
> CustomFootprint = 1
> CustomZoning = 1
> ActiveZoneIndex = 62
> FloorArea = 11008.1
> FloorPerimLen = 840.296
> LastFootprint = 5
> OverhangOption = "None"
> GTCCategory[2] = "- select another -"
> PercentGlass2[1] = 0
> PercentGlass3[1] = 20
> NumExtDoors1[1] = 0
> NumExtDoors2[1] = 0
> NumExtDoors3[1] = 0
> DoorWidth[1] = 3
> OpaqueDoorType[1] = "Steel Hollow core w/o Brk"
> SkyZonesCurrent = 1
> SkyltZones[1] = 1
> SkyltZones[2] = 1
> SkyltZones[3] = 1
> SkyltZones[4] = 1
> SkyltZones[5] = 1
> SkyltZones[6] = 1
> SkyltZones[7] = 1
> SkyltZones[8] = 1
> SkyltZones[9] = 1
> SkyltZones[10] = 1
> SkyltZones[11] = 1
> SkyltZones[12] = 1
> SkyltZones[13] = 1
> SkyltZones[14] = 1
> SkyltZones[15] = 1
> SkyltZones[16] = 1
> SkyltZones[17] = 1
> SkyltZones[18] = 1
> SkyltZones[19] = 1
> SkyltZones[20] = 1
> SkyltZones[21] = 1
> SkyltZones[22] = 1
> SkyltZones[23] = 1
> SkyltZones[24] = 1
> SkyltZones[25] = 1
> SkyltZones[26] = 1
> SkyltZones[27] = 1
> SkyltZones[28] = 1
> SkyltZones[29] = 1
> SkyltZones[30] = 1
> SkyltZones[31] = 1
> SkyltZones[32] = 1
> SkyltZones[33] = 1
> SkyltZones[34] = 1
> SkyltZones[35] = 1
> SkyltZones[36] = 1
> SkyltZones[37] = 1
> SkyltZones[38] = 1
> SkyltZones[39] = 1
> SkyltZones[40] = 1
> SkyltZones[41] = 1
> SkyltZones[42] = 1
> SkyltZones[43] = 1
> SkyltZones[44] = 1
> SkyltZones[45] = 1
> SkyltZones[46] = 1
> SkyltZones[47] = 1
> SkyltZones[48] = 1
> SkyltZones[49] = 1
> SkyltZones[50] = 1
> SkyltZones[51] = 1
> SkyltZones[52] = 1
> SkyltZones[53] = 1
> SkyltZones[54] = 1
> SkyltZones[55] = 1
> SkyltZones[56] = 1
> SkyltZones[57] = 1
> SkyltZones[58] = 1
> SkyltZones[59] = 1
> SkyltZones[60] = 1
> SkyltZones[61] = 1
> SkyltZones[62] = 1
> SkyPosCurrent = 1
> DayZonesCurrent[3] = 1
> DayltZones[1] = 1
> DayltZones[2] = 1
> DayltZones[3] = 1
> DayltZones[4] = 1
> DayltZones[5] = 0
> DayltZones[401] = 1
> DayltZones[402] = 1
> DayltZones[403] = 0
> DayltZones[404] = 0
> DayltZones[405] = 1
> DayltZones[406] = 1
> DayltZones[407] = 1
> DayltZones[408] = 1
> DayltZones[409] = 1
> DayltZones[410] = 1
> DayltZones[411] = 1
> DayltZones[412] = 1
> DayltZones[413] = 0
> DayltZones[414] = 1
> DayltZones[415] = 1
> DayltZones[416] = 1
> DayltZones[417] = 1
> DayltZones[418] = 1
> DayltZones[419] = 1
> DayltZones[420] = 1
> DayltZones[421] = 1
> DayltZones[422] = 1
> DayltZones[423] = 1
> DayltZones[424] = 0
> DayltZones[425] = 1
> DayltZones[426] = 0
> DayltZones[427] = 1
> DayltZones[428] = 1
> DayltZones[429] = 1
> DayltZones[430] = 1
> DayltZones[431] = 1
> DayltZones[432] = 1
> DayltZones[433] = 1
> DayltZones[434] = 1
> DayltZones[435] = 0
> DayltZones[436] = 0
> DayltZones[437] = 0
> DayltZones[438] = 0
> DayltZones[439] = 0
> DayltZones[440] = 0
> DayltZones[441] = 0
> DayltZones[442] = 0
> DayltZones[443] = 0
> DayltZones[444] = 0
> DayltZones[445] = 0
> DayltZones[446] = 0
> DayltZones[447] = 0
> DayltZones[448] = 0
> DayltZones[449] = 0
> DayltZones[450] = 0
> DayltZones[451] = 0
> DayltZones[452] = 0
> DayltZones[453] = 1
> DayltZones[454] = 1
> DayltZones[455] = 1
> DayltZones[456] = 1
> DayltZones[457] = 1
> DayltZones[458] = 1
> DayltZones[459] = 1
> DayltZones[460] = 1
> DayltZones[461] = 1
> DayltZones[462] = 1
> WinDoorCurrent = 1
> DetailsCurrent = ( 1, 1, 1 )
> BDLNumDayltCtrls[1] = 0
> BDLNumDayltCtrls[2] = 0
> BDLNumDayltCtrls[3] = 0
> BDLNumDayltCtrls[4] = 0
> BDLNumDayltCtrls[5] = 0
> BDLNumDayltCtrls[401] = 0
> BDLNumDayltCtrls[402] = 0
> BDLNumDayltCtrls[403] = 0
> BDLNumDayltCtrls[404] = 0
> BDLNumDayltCtrls[405] = 0
> BDLNumDayltCtrls[406] = 0
> BDLNumDayltCtrls[407] = 0
> BDLNumDayltCtrls[408] = 0
> BDLNumDayltCtrls[409] = 0
> BDLNumDayltCtrls[410] = 0
> BDLNumDayltCtrls[411] = 0
> BDLNumDayltCtrls[412] = 0
> BDLNumDayltCtrls[413] = 0
> BDLNumDayltCtrls[414] = 0
> BDLNumDayltCtrls[415] = 0
> BDLNumDayltCtrls[416] = 0
> BDLNumDayltCtrls[417] = 0
> BDLNumDayltCtrls[418] = 0
> BDLNumDayltCtrls[419] = 0
> BDLNumDayltCtrls[420] = 0
> BDLNumDayltCtrls[421] = 0
> BDLNumDayltCtrls[422] = 0
> BDLNumDayltCtrls[423] = 0
> BDLNumDayltCtrls[424] = 0
> BDLNumDayltCtrls[425] = 0
> BDLNumDayltCtrls[426] = 0
> BDLNumDayltCtrls[427] = 0
> BDLNumDayltCtrls[428] = 0
> BDLNumDayltCtrls[429] = 0
> BDLNumDayltCtrls[430] = 0
> BDLNumDayltCtrls[431] = 0
> BDLNumDayltCtrls[432] = 0
> BDLNumDayltCtrls[433] = 0
> BDLNumDayltCtrls[434] = 0
> BDLNumDayltCtrls[435] = 0
> BDLNumDayltCtrls[436] = 0
> BDLNumDayltCtrls[437] = 0
> BDLNumDayltCtrls[438] = 0
> BDLNumDayltCtrls[439] = 0
> BDLNumDayltCtrls[440] = 0
> BDLNumDayltCtrls[441] = 0
> BDLNumDayltCtrls[442] = 0
> BDLNumDayltCtrls[443] = 0
> BDLNumDayltCtrls[444] = 0
> BDLNumDayltCtrls[445] = 0
> BDLNumDayltCtrls[446] = 0
> BDLNumDayltCtrls[447] = 0
> BDLNumDayltCtrls[448] = 0
> BDLNumDayltCtrls[449] = 0
> BDLNumDayltCtrls[450] = 0
> BDLNumDayltCtrls[451] = 0
> BDLNumDayltCtrls[452] = 0
> BDLNumDayltCtrls[453] = 0
> BDLNumDayltCtrls[454] = 0
> BDLNumDayltCtrls[455] = 0
> BDLNumDayltCtrls[456] = 0
> BDLNumDayltCtrls[457] = 0
> BDLNumDayltCtrls[458] = 0
> BDLNumDayltCtrls[459] = 0
> BDLNumDayltCtrls[460] = 0
> BDLNumDayltCtrls[461] = 0
> BDLNumDayltCtrls[462] = 0
> OccShape = ( "EL1 Occup Profile (S1)", "EL1 Occup Profile (S2)",
> "EL1 Occup Profile (S3)" )
> ILShape = ( "EL1 InsLtg Profile (S1)", "EL1 InsLtg Profile (S2)",
> "EL1 InsLtg Profile (S3)" )
> ELElecIntens = 0.2
> ELDayShapes = ( "EL1 ExtLtg DayShape (Jan)",
> "EL1 ExtLtg DayShape (Feb)",
> "EL1 ExtLtg DayShape (Mar)",
> "EL1 ExtLtg DayShape (Apr)",
> "EL1 ExtLtg DayShape (May)",
> "EL1 ExtLtg DayShape (Jun)",
> "EL1 ExtLtg DayShape (Jul)",
> "EL1 ExtLtg DayShape (Aug)",
> "EL1 ExtLtg DayShape (Sep)",
> "EL1 ExtLtg DayShape (Oct)",
> "EL1 ExtLtg DayShape (Nov)",
> "EL1 ExtLtg DayShape (Dec)" )
> OEShape = ( "EL1 OffEq Profile (S1)", "EL1 OffEq Profile (S2)",
> "EL1 OffEq Profile (S3)" )
> CEShape = ( "EL1 CookEq Profile (S1)", "EL1 CookEq Profile (S2)",
> "EL1 CookEq Profile (S3)" )
> MiscShape = ( "EL1 Misc Profile (S1)", "EL1 Misc Profile (S2)",
> "EL1 Misc Profile (S3)" )
> RFDayShapes = ( "EL1 Refrig DayShape (Jan)",
> "EL1 Refrig DayShape (Feb)",
> "EL1 Refrig DayShape (Mar)",
> "EL1 Refrig DayShape (Apr)",
> "EL1 Refrig DayShape (May)",
> "EL1 Refrig DayShape (Jun)",
> "EL1 Refrig DayShape (Jul)",
> "EL1 Refrig DayShape (Aug)",
> "EL1 Refrig DayShape (Sep)",
> "EL1 Refrig DayShape (Oct)",
> "EL1 Refrig DayShape (Nov)",
> "EL1 Refrig DayShape (Dec)" )
> DHWShape = ( "EL1 DHW Profile (S1)", "EL1 DHW Profile (S2)",
> "EL1 DHW Profile (S3)" )
> TLShape = ( "EL1 TskLtg Profile (S1)", "EL1 TskLtg Profile (S2)",
> "EL1 TskLtg Profile (S3)" )
> TLElecIntens[1] = 0.02
> SCRShape = ( "EL1 S-C Refrig Profile (S1)",
> "EL1 S-C Refrig Profile (S2)",
> "EL1 S-C Refrig Profile (S3)" )
> DaylitAreaCurrent[3] = 1
> HasPitchedRoof = 0
> RoofZoneErrorCode = 4
> RoofEndIsGable[28] = 0
> RoofEndIsGable[36] = 0
> BDBaseUpdateFlag[3] = 0
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S1)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jan)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Feb)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Mar)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Apr)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (May)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jun)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Jul)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Aug)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Sep)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Oct)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Nov)"
> ..
>
> DayShape "EL1 ExtLtg DayShape (Dec)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S1)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S1)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S1)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S1)"
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S2)"
> ..
>
> ShapeWiz "EL1 InsLtg Profile (S3)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S2)"
> ..
>
> ShapeWiz "EL1 OffEq Profile (S3)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S1)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S2)"
> ..
>
> ShapeWiz "EL1 CookEq Profile (S3)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jan)"
> ..
>
> DayShape "EL1 Refrig DayShape (Feb)"
> ..
>
> DayShape "EL1 Refrig DayShape (Mar)"
> ..
>
> DayShape "EL1 Refrig DayShape (Apr)"
> ..
>
> DayShape "EL1 Refrig DayShape (May)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jun)"
> ..
>
> DayShape "EL1 Refrig DayShape (Jul)"
> ..
>
> DayShape "EL1 Refrig DayShape (Aug)"
> ..
>
> DayShape "EL1 Refrig DayShape (Sep)"
> ..
>
> DayShape "EL1 Refrig DayShape (Oct)"
> ..
>
> DayShape "EL1 Refrig DayShape (Nov)"
> ..
>
> DayShape "EL1 Refrig DayShape (Dec)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S2)"
> ..
>
> ShapeWiz "EL1 Misc Profile (S3)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S2)"
> ..
>
> ShapeWiz "EL1 DHW Profile (S3)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S2)"
> ..
>
> ShapeWiz "EL1 Occup Profile (S3)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S1)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S2)"
> ..
>
> ShapeWiz "EL1 S-C Refrig Profile (S3)"
> ..
>
> ZnGrpWiz "EL1 Ground Floor"
> ShortName = "GndFlr"
> ..
>
> CustomZone "Custom Zone 1"
> NumVerts = 8
> X[1] = 6.85
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 40.35
> X[5] = 32.5
> X[6] = 16.3
> X[7] = 18.5
> X[8] = 18.5
> Y[1] = 35.45
> Y[2] = 35.45
> Y[3] = 56.45
> Y[4] = 56.65
> Y[5] = 56.65
> Y[6] = 56.65
> Y[7] = 52.5
> Y[8] = 40.35
> ..
>
> CustomZone "Custom Zone 2"
> NumVerts = 4
> X[1] = 6.85
> X[2] = 6.85
> X[3] = 16.3
> X[4] = 17.5
> Y[1] = 67.95
> Y[2] = 56.75
> Y[3] = 56.65
> Y[4] = 67.95
> ..
>
> CustomZone "Custom Zone 3"
> NumVerts = 5
> X[1] = 17.5
> X[2] = 16.3
> X[3] = 32.5
> X[4] = 33.35
> X[5] = 27.05
> Y[1] = 67.95
> Y[2] = 56.65
> Y[3] = 56.65
> Y[4] = 67.5
> Y[5] = 67.45
> ..
>
> CustomZone "Custom Zone 4"
> NumVerts = 4
> X[1] = 32.5
> X[2] = 40.35
> X[3] = 41
> X[4] = 33.35
> Y[1] = 56.65
> Y[2] = 56.65
> Y[3] = 67.5
> Y[4] = 67.5
> ..
>
> CustomZone "Custom Zone 5"
> NumVerts = 4
> X[1] = 41
> X[2] = 40.35
> X[3] = 46.5
> X[4] = 46.5
> Y[1] = 67.5
> Y[2] = 56.65
> Y[3] = 56.45
> Y[4] = 67.45
> ..
>
> CustomZone "Custom Zone 6"
> NumVerts = 10
> X[1] = 46.5
> X[2] = 46.5
> X[3] = 27.9
> X[4] = 27.85
> X[5] = 27.85
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.05
> X[9] = 33.35
> X[10] = 41
> Y[1] = 67.45
> Y[2] = 92.8
> Y[3] = 92.75
> Y[4] = 88.1
> Y[5] = 81.7
> Y[6] = 78.1
> Y[7] = 71.8
> Y[8] = 67.45
> Y[9] = 67.5
> Y[10] = 67.5
> ..
>
> CustomZone "Custom Zone 7"
> NumVerts = 8
> X[1] = 27.9
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 25.85
> X[5] = 27.85
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> Y[1] = 92.75
> Y[2] = 92.8
> Y[3] = 117.8
> Y[4] = 118.15
> Y[5] = 113.45
> Y[6] = 107.2
> Y[7] = 103.45
> Y[8] = 97.2
> ..
>
> CustomZone "Custom Zone 8"
> NumVerts = 5
> X[1] = 25.85
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 25.65
> X[5] = 25.5
> Y[1] = 118.15
> Y[2] = 117.8
> Y[3] = 129.3
> Y[4] = 129.15
> Y[5] = 123.45
> ..
>
> CustomZone "Custom Zone 9"
> NumVerts = 4
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.4
> X[4] = 25.5
> Y[1] = 129.15
> Y[2] = 129.1
> Y[3] = 123.5
> Y[4] = 123.45
> ..
>
> CustomZone "Custom Zone 10"
> NumVerts = 4
> X[1] = 17.4
> X[2] = 17.45
> X[3] = 25.85
> X[4] = 25.5
> Y[1] = 123.5
> Y[2] = 118.2
> Y[3] = 118.15
> Y[4] = 123.45
> ..
>
> CustomZone "Custom Zone 11"
> NumVerts = 9
> X[1] = 25.65
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 42.65
> X[5] = 27.9
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 27.85
> Y[1] = 129.15
> Y[2] = 129.3
> Y[3] = 155.15
> Y[4] = 155.15
> Y[5] = 154.1
> Y[6] = 149.6
> Y[7] = 143.5
> Y[8] = 139.7
> Y[9] = 133.5
> ..
>
> CustomZone "Custom Zone 12"
> NumVerts = 5
> X[1] = 42.6
> X[2] = 18
> X[3] = 17.45
> X[4] = 27.9
> X[5] = 42.65
> Y[1] = 164.5
> Y[2] = 164.5
> Y[3] = 153.65
> Y[4] = 154.1
> Y[5] = 155.15
> ..
>
> CustomZone "Custom Zone 13"
> NumVerts = 4
> X[1] = 18
> X[2] = 42.6
> X[3] = 42.7
> X[4] = 18
> Y[1] = 164.5
> Y[2] = 164.5
> Y[3] = 167.05
> Y[4] = 166.5
> ZoneType = "Unconditioned"
> ..
>
> CustomZone "Custom Zone 14"
> NumVerts = 5
> X[1] = 42.7
> X[2] = 42.65
> X[3] = 27.05
> X[4] = 17.5
> X[5] = 18
> Y[1] = 167.05
> Y[2] = 175.85
> Y[3] = 176.85
> Y[4] = 177.4
> Y[5] = 166.5
> ..
>
> CustomZone "Custom Zone 15"
> NumVerts = 4
> X[1] = 13.5
> X[2] = 13.1
> X[3] = 6.8
> X[4] = 6.8
> Y[1] = 169.9
> Y[2] = 177.4
> Y[3] = 177.4
> Y[4] = 170.45
> ZoneType = "Conditioned"
> ..
>
> CustomZone "Custom Zone 16"
> NumVerts = 8
> X[1] = 17.5
> X[2] = 13.1
> X[3] = 13.5
> X[4] = 6.8
> X[5] = 6.8
> X[6] = 17.45
> X[7] = 18
> X[8] = 18
> Y[1] = 177.4
> Y[2] = 177.4
> Y[3] = 169.9
> Y[4] = 170.45
> Y[5] = 153.65
> Y[6] = 153.65
> Y[7] = 164.5
> Y[8] = 166.5
> ..
>
> CustomZone "Custom Zone 17"
> NumVerts = 9
> X[1] = 27.05
> X[2] = 42.65
> X[3] = 46.5
> X[4] = 46.5
> X[5] = 25.65
> X[6] = 27.85
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 27.85
> Y[1] = 176.85
> Y[2] = 175.85
> Y[3] = 175.9
> Y[4] = 201.9
> Y[5] = 201.9
> Y[6] = 197.5
> Y[7] = 191.25
> Y[8] = 187.55
> Y[9] = 181.25
> ..
>
> CustomZone "Custom Zone 18"
> NumVerts = 5
> X[1] = 46.5
> X[2] = 46.5
> X[3] = 25.65
> X[4] = 25.15
> X[5] = 25.65
> Y[1] = 201.9
> Y[2] = 213.2
> Y[3] = 213.2
> Y[4] = 207.4
> Y[5] = 201.9
> ..
>
> CustomZone "Custom Zone 19"
> NumVerts = 4
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.4
> X[4] = 25.15
> Y[1] = 213.2
> Y[2] = 213.2
> Y[3] = 207.75
> Y[4] = 207.4
> ..
>
> CustomZone "Custom Zone 20"
> NumVerts = 4
> X[1] = 25.15
> X[2] = 17.4
> X[3] = 17.45
> X[4] = 25.65
> Y[1] = 207.4
> Y[2] = 207.75
> Y[3] = 201.8
> Y[4] = 201.9
> ..
>
> CustomZone "Custom Zone 21"
> NumVerts = 9
> X[1] = 25.65
> X[2] = 46.5
> X[3] = 46.5
> X[4] = 43.4
> X[5] = 27.85
> X[6] = 27.65
> X[7] = 27.65
> X[8] = 27.7
> X[9] = 27.7
> Y[1] = 213.2
> Y[2] = 213.2
> Y[3] = 236.1
> Y[4] = 238.55
> Y[5] = 238.5
> Y[6] = 233.8
> Y[7] = 227.55
> Y[8] = 223.75
> Y[9] = 217.5
> ..
>
> CustomZone "Custom Zone 22"
> NumVerts = 14
> X[1] = 27.65
> X[2] = 27.85
> X[3] = 43.4
> X[4] = 46.5
> X[5] = 55.55
> X[6] = 58.5
> X[7] = 45.5
> X[8] = 46
> X[9] = 46.5
> X[10] = 46.5
> X[11] = 17.5
> X[12] = 27.4
> X[13] = 27.4
> X[14] = 27.65
> Y[1] = 245.8
> Y[2] = 238.5
> Y[3] = 238.55
> Y[4] = 236.1
> Y[5] = 232.15
> Y[6] = 238.5
> Y[7] = 244.2
> Y[8] = 254.9
> Y[9] = 267.75
> Y[10] = 273.55
> Y[11] = 273.55
> Y[12] = 265.3
> Y[13] = 259.05
> Y[14] = 252.05
> ..
>
> CustomZone "Custom Zone 23"
> NumVerts = 5
> X[1] = 46.5
> X[2] = 46
> X[3] = 57.2
> X[4] = 59.3
> X[5] = 61.45
> Y[1] = 267.75
> Y[2] = 254.9
> Y[3] = 250.55
> Y[4] = 255.45
> Y[5] = 261.25
> ..
>
> CustomZone "Custom Zone 24"
> NumVerts = 5
> X[1] = 46
> X[2] = 45.5
> X[3] = 58.5
> X[4] = 62.5
> X[5] = 57.2
> Y[1] = 254.9
> Y[2] = 244.2
> Y[3] = 238.5
> Y[4] = 247.7
> Y[5] = 250.55
> ..
>
> CustomZone "Custom Zone 25"
> NumVerts = 4
> X[1] = 67.55
> X[2] = 61.45
> X[3] = 59.3
> X[4] = 65.1
> Y[1] = 258.5
> Y[2] = 261.25
> Y[3] = 255.45
> Y[4] = 252.7
> ..
>
> CustomZone "Custom Zone 26"
> NumVerts = 4
> X[1] = 59.3
> X[2] = 57.2
> X[3] = 62.5
> X[4] = 65.1
> Y[1] = 255.45
> Y[2] = 250.55
> Y[3] = 247.7
> Y[4] = 252.7
> ..
>
> CustomZone "Custom Zone 27"
> NumVerts = 10
> X[1] = 55.55
> X[2] = 78.9
> X[3] = 87.25
> X[4] = 82.45
> X[5] = 76.45
> X[6] = 73.35
> X[7] = 67.55
> X[8] = 65.1
> X[9] = 62.5
> X[10] = 58.5
> Y[1] = 232.15
> Y[2] = 222
> Y[3] = 241.05
> Y[4] = 241
> Y[5] = 243.4
> Y[6] = 244.9
> Y[7] = 247.5
> Y[8] = 252.7
> Y[9] = 247.7
> Y[10] = 238.5
> ..
>
> CustomZone "Custom Zone 28"
> NumVerts = 4
> X[1] = 90.5
> X[2] = 87.25
> X[3] = 92.8
> X[4] = 95.65
> Y[1] = 248.55
> Y[2] = 241.05
> Y[3] = 239.2
> Y[4] = 246.3
> ..
>
> CustomZone "Custom Zone 29"
> NumVerts = 5
> X[1] = 78.9
> X[2] = 89.3
> X[3] = 97.55
> X[4] = 92.8
> X[5] = 87.25
> Y[1] = 222
> Y[2] = 217.45
> Y[3] = 236.4
> Y[4] = 239.2
> Y[5] = 241.05
> ..
>
> CustomZone "Custom Zone 30"
> NumVerts = 4
> X[1] = 92.8
> X[2] = 97.55
> X[3] = 100.35
> X[4] = 95.65
> Y[1] = 239.2
> Y[2] = 236.4
> Y[3] = 244.3
> Y[4] = 246.3
> ..
>
> CustomZone "Custom Zone 31"
> NumVerts = 10
> X[1] = 100.85
> X[2] = 97.55
> X[3] = 89.3
> X[4] = 113.15
> X[5] = 114.65
> X[6] = 118
> X[7] = 119.7
> X[8] = 115.85
> X[9] = 109.75
> X[10] = 106.45
> Y[1] = 233
> Y[2] = 236.4
> Y[3] = 217.45
> Y[4] = 207.05
> Y[5] = 210.55
> Y[6] = 219.45
> Y[7] = 224.5
> Y[8] = 226.25
> Y[9] = 228.9
> Y[10] = 230.3
> MultiLevel = 0
> ..
>
> CustomZone "Custom Zone 32"
> NumVerts = 5
> X[1] = 123.8
> X[2] = 119.7
> X[3] = 118
> X[4] = 127.4
> X[5] = 133.2
> Y[1] = 234.05
> Y[2] = 224.5
> Y[3] = 219.45
> Y[4] = 215.35
> Y[5] = 229.95
> ..
>
> CustomZone "Custom Zone 33"
> NumVerts = 4
> X[1] = 118
> X[2] = 114.65
> X[3] = 123.1
> X[4] = 127.4
> Y[1] = 219.45
> Y[2] = 210.55
> Y[3] = 206.85
> Y[4] = 215.35
> ..
>
> CustomZone "Custom Zone 34"
> NumVerts = 9
> X[1] = 121.6
> X[2] = 145.9
> X[3] = 161.75
> X[4] = 153.45
> X[5] = 150.5
> X[6] = 139.6
> X[7] = 133.2
> X[8] = 127.4
> X[9] = 123.1
> Y[1] = 203.35
> Y[2] = 192.75
> Y[3] = 229.1
> Y[4] = 228
> Y[5] = 221.3
> Y[6] = 225.9
> Y[7] = 229.95
> Y[8] = 215.35
> Y[9] = 206.85
> ..
>
> CustomZone "Custom Zone 35"
> NumVerts = 4
> X[1] = 10.65
> X[2] = 10.65
> X[3] = 18.5
> X[4] = 18.5
> Y[1] = 52.5
> Y[2] = 40.35
> Y[3] = 40.35
> Y[4] = 52.5
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 36"
> NumVerts = 4
> X[1] = 27.85
> X[2] = 19.2
> X[3] = 19.2
> X[4] = 27.85
> Y[1] = 88.1
> Y[2] = 88.1
> Y[3] = 81.7
> Y[4] = 81.7
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 37"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 71.85
> Y[2] = 71.8
> Y[3] = 78.1
> Y[4] = 78.1
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 38"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 97.2
> Y[2] = 97.2
> Y[3] = 103.45
> Y[4] = 103.45
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 39"
> NumVerts = 4
> X[1] = 27.85
> X[2] = 27.85
> X[3] = 19.2
> X[4] = 19.2
> Y[1] = 107.2
> Y[2] = 113.45
> Y[3] = 113.45
> Y[4] = 107.2
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 40"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 19.2
> X[3] = 27.85
> X[4] = 27.85
> Y[1] = 149.75
> Y[2] = 143.5
> Y[3] = 143.5
> Y[4] = 149.6
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 41"
> NumVerts = 4
> X[1] = 19.2
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19.2
> Y[1] = 133.5
> Y[2] = 133.5
> Y[3] = 139.7
> Y[4] = 139.7
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 42"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19
> Y[1] = 181.25
> Y[2] = 181.25
> Y[3] = 187.55
> Y[4] = 187.55
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 43"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.85
> X[3] = 27.85
> X[4] = 19
> Y[1] = 191.25
> Y[2] = 191.25
> Y[3] = 197.5
> Y[4] = 197.5
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 44"
> NumVerts = 4
> X[1] = 19
> X[2] = 19
> X[3] = 27.65
> X[4] = 27.65
> Y[1] = 233.8
> Y[2] = 227.55
> Y[3] = 227.55
> Y[4] = 233.8
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 45"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.65
> X[3] = 27.65
> X[4] = 19
> Y[1] = 245.8
> Y[2] = 245.8
> Y[3] = 252.05
> Y[4] = 252.05
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 46"
> NumVerts = 4
> X[1] = 19
> X[2] = 27.4
> X[3] = 27.4
> X[4] = 19
> Y[1] = 259.05
> Y[2] = 259.05
> Y[3] = 265.3
> Y[4] = 265.3
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 47"
> NumVerts = 4
> X[1] = 71
> X[2] = 67.55
> X[3] = 73.35
> X[4] = 76.8
> Y[1] = 255.4
> Y[2] = 247.5
> Y[3] = 244.9
> Y[4] = 252.8
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 48"
> NumVerts = 4
> X[1] = 76.45
> X[2] = 82.45
> X[3] = 85.9
> X[4] = 80.15
> Y[1] = 243.4
> Y[2] = 241
> Y[3] = 248.95
> Y[4] = 251.45
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 49"
> NumVerts = 4
> X[1] = 104.3
> X[2] = 100.85
> X[3] = 106.45
> X[4] = 110.05
> Y[1] = 240.75
> Y[2] = 233
> Y[3] = 230.3
> Y[4] = 238.4
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 50"
> NumVerts = 4
> X[1] = 109.75
> X[2] = 115.85
> X[3] = 119.2
> X[4] = 113.45
> Y[1] = 228.9
> Y[2] = 226.25
> Y[3] = 234.4
> Y[4] = 236.9
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 51"
> NumVerts = 4
> X[1] = 142.9
> X[2] = 139.6
> X[3] = 150.5
> X[4] = 153.45
> Y[1] = 232.6
> Y[2] = 225.9
> Y[3] = 221.3
> Y[4] = 228
> MultiLevel = 1
> ..
>
> ZnGrpWiz "Exhausted Zone Group 2"
> ShortName = "GndFlr"
> HaveExhaustFans = 1
> XFanFlow = 660
> XFanMotorEff = "High"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S1)"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S2)"
> ..
>
> ShapeWiz "EL1 TskLtg Profile (S3)"
> ..
>
> CustomZone "Custom Zone 52"
> NumVerts = 4
> X[1] = 19.05
> X[2] = 27.7
> X[3] = 27.7
> X[4] = 19
> Y[1] = 217.5
> Y[2] = 217.5
> Y[3] = 223.75
> Y[4] = 223.75
> MultiLevel = 1
> ..
>
> CustomZone "Custom Zone 53"
> NumVerts = 12
> X[1] = 27.85
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 25.65
> X[5] = 27.7
> X[6] = 19.05
> X[7] = 19
> X[8] = 27.7
> X[9] = 27.65
> X[10] = 19
> X[11] = 19
> X[12] = 27.65
> Y[1] = 238.5
> Y[2] = 238.2
> Y[3] = 213.2
> Y[4] = 213.2
> Y[5] = 217.5
> Y[6] = 217.5
> Y[7] = 223.75
> Y[8] = 223.75
> Y[9] = 227.55
> Y[10] = 227.55
> Y[11] = 233.8
> Y[12] = 233.8
> ..
>
> CustomZone "Custom Zone 54"
> NumVerts = 12
> X[1] = 25.65
> X[2] = 17.45
> X[3] = 17.5
> X[4] = 27.05
> X[5] = 27.85
> X[6] = 19
> X[7] = 19
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19
> X[11] = 19
> X[12] = 27.85
> Y[1] = 201.9
> Y[2] = 201.8
> Y[3] = 177.4
> Y[4] = 176.85
> Y[5] = 181.25
> Y[6] = 181.25
> Y[7] = 187.55
> Y[8] = 187.55
> Y[9] = 191.25
> Y[10] = 191.25
> Y[11] = 197.5
> Y[12] = 197.5
> ..
>
> CustomZone "Custom Zone 55"
> NumVerts = 12
> X[1] = 27.9
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 25.65
> X[5] = 27.85
> X[6] = 19.2
> X[7] = 19.2
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19.2
> X[11] = 19.2
> X[12] = 27.85
> Y[1] = 154.1
> Y[2] = 153.65
> Y[3] = 129.1
> Y[4] = 129.15
> Y[5] = 133.5
> Y[6] = 133.5
> Y[7] = 139.7
> Y[8] = 139.7
> Y[9] = 143.5
> Y[10] = 143.5
> Y[11] = 149.75
> Y[12] = 149.6
> ..
>
> CustomZone "Custom Zone 56"
> NumVerts = 12
> X[1] = 25.85
> X[2] = 17.45
> X[3] = 17.45
> X[4] = 27.9
> X[5] = 27.85
> X[6] = 19.2
> X[7] = 19.2
> X[8] = 27.85
> X[9] = 27.85
> X[10] = 19.2
> X[11] = 19.2
> X[12] = 27.85
> Y[1] = 118.15
> Y[2] = 118.2
> Y[3] = 92.8
> Y[4] = 92.75
> Y[5] = 97.2
> Y[6] = 97.2
> Y[7] = 103.45
> Y[8] = 103.45
> Y[9] = 107.2
> Y[10] = 107.2
> Y[11] = 113.45
> Y[12] = 113.45
> ..
>
> CustomZone "Custom Zone 57"
> NumVerts = 12
> X[1] = 17.45
> X[2] = 17.5
> X[3] = 27.05
> X[4] = 27.85
> X[5] = 19.2
> X[6] = 19.2
> X[7] = 27.85
> X[8] = 27.85
> X[9] = 19.2
> X[10] = 19.2
> X[11] = 27.85
> X[12] = 27.9
> Y[1] = 92.8
> Y[2] = 67.95
> Y[3] = 67.45
> Y[4] = 71.8
> Y[5] = 71.85
> Y[6] = 78.1
> Y[7] = 78.1
> Y[8] = 81.7
> Y[9] = 81.7
> Y[10] = 88.1
> Y[11] = 88.1
> Y[12] = 92.75
> ..
>
> CustomZone "Custom Zone 58"
> NumVerts = 7
> X[1] = 16.3
> X[2] = 6.85
> X[3] = 6.85
> X[4] = 18.5
> X[5] = 10.65
> X[6] = 10.65
> X[7] = 18.5
> Y[1] = 56.65
> Y[2] = 56.75
> Y[3] = 35.45
> Y[4] = 40.35
> Y[5] = 40.35
> Y[6] = 52.5
> Y[7] = 52.5
> ..
>
> CustomZone "Custom Zone 59"
> NumVerts = 11
> X[1] = 17.5
> X[2] = 17.45
> X[3] = 27.85
> X[4] = 27.65
> X[5] = 19
> X[6] = 19
> X[7] = 27.65
> X[8] = 27.4
> X[9] = 19
> X[10] = 19
> X[11] = 27.4
> Y[1] = 273.55
> Y[2] = 238.2
> Y[3] = 238.5
> Y[4] = 245.8
> Y[5] = 245.8
> Y[6] = 252.05
> Y[7] = 252.05
> Y[8] = 259.05
> Y[9] = 259.05
> Y[10] = 265.3
> Y[11] = 265.3
> ..
>
> CustomZone "Custom Zone 60"
> NumVerts = 12
> X[1] = 67.55
> X[2] = 65.1
> X[3] = 67.55
> X[4] = 71
> X[5] = 76.8
> X[6] = 73.35
> X[7] = 76.45
> X[8] = 80.15
> X[9] = 85.9
> X[10] = 82.45
> X[11] = 87.25
> X[12] = 90.5
> Y[1] = 258.5
> Y[2] = 252.7
> Y[3] = 247.5
> Y[4] = 255.4
> Y[5] = 252.8
> Y[6] = 244.9
> Y[7] = 243.4
> Y[8] = 251.45
> Y[9] = 248.95
> Y[10] = 241
> Y[11] = 241.05
> Y[12] = 248.55
> ..
>
> CustomZone "Custom Zone 61"
> NumVerts = 12
> X[1] = 100.35
> X[2] = 97.55
> X[3] = 100.85
> X[4] = 104.3
> X[5] = 110.05
> X[6] = 106.45
> X[7] = 109.75
> X[8] = 113.45
> X[9] = 119.2
> X[10] = 115.85
> X[11] = 119.7
> X[12] = 123.8
> Y[1] = 244.3
> Y[2] = 236.4
> Y[3] = 233
> Y[4] = 240.75
> Y[5] = 238.4
> Y[6] = 230.3
> Y[7] = 228.9
> Y[8] = 236.9
> Y[9] = 234.4
> Y[10] = 226.25
> Y[11] = 224.5
> Y[12] = 234.05
> ..
>
> CustomZone "Custom Zone 62"
> NumVerts = 6
> X[1] = 161.75
> X[2] = 137.45
> X[3] = 133.2
> X[4] = 139.6
> X[5] = 142.9
> X[6] = 153.45
> Y[1] = 229.1
> Y[2] = 239.7
> Y[3] = 229.95
> Y[4] = 225.9
> Y[5] = 232.6
> Y[6] = 228
> ..
>
> ZnGrpWiz "ERV Zone Group 3"
> ShortName = "GndFlr"
> AssignedSystem = "ERV"
> ..
>
> ZnGrpWiz "Unconditioned Zone Group 4"
> ShortName = "GndFlr"
> IsConditioned = 0
> ..
>
> DiagData "Bldg Envelope & Loads 1 Diag Data"
> PolyWndShowGrid = 0
> PolyWndGridRes = 2
> PolyWndDWGSnapRad = 0.25
> PolyWndPlySnapRad = 0.25
> PolyWndLwrLeftX = -149.2
> PolyWndLwrLeftY = 9.45
> PolyWndWidth = 466.333
> PolyWndSnapOrder = ( 2, 1, 0 )
> ShowCADLayer[1] = 1
> ShowCADLayer[2] = 0
> ShowCADLayer[3] = 0
> ShowCADLayer[4] = 1
> ShowCADLayer[5] = 1
> ShowCADLayer[6] = 1
> ShowCADLayer[7] = 1
> ShowCADLayer[8] = 1
> ShowCADLayer[9] = 1
> ShowCADLayer[10] = 1
> ShowCADLayer[11] = 1
> ShowCADLayer[12] = 1
> ShowCADLayer[13] = 1
> ShowCADLayer[14] = 1
> ShowCADLayer[15] = 1
> ShowCADLayer[16] = 1
> ShowCADLayer[17] = 1
> ShowCADLayer[18] = 1
> ShowCADLayer[19] = 1
> ShowCADLayer[20] = 1
> ShowCADLayer[21] = 1
> ShowCADLayer[22] = 1
> ShowCADLayer[23] = 1
> ShowCADLayer[24] = 1
> ShowCADLayer[25] = 1
> ShowCADLayer[26] = 1
> ShowCADLayer[27] = 1
> ShowCADLayer[28] = 1
> ShowCADLayer[29] = 1
> ShowCADLayer[30] = 1
> ShowCADLayer[31] = 1
> ShowCADLayer[32] = 1
> ShowCADLayer[33] = 1
> ShowCADLayer[34] = 1
> ShowCADLayer[35] = 1
> ShowCADLayer[36] = 1
> ShowCADLayer[37] = 0
> ShowCADLayer[38] = 1
> ShowCADLayer[39] = 1
> ShowCADLayer[40] = 1
> ShowCADLayer[41] = 1
> ShowCADLayer[42] = 1
> ShowCADLayer[43] = 1
> ShowCADLayer[44] = 1
> ShowCADLayer[45] = 1
> ShowCADLayer[46] = 1
> ShowCADLayer[47] = 1
> ShowCADLayer[48] = 1
> ShowCADLayer[49] = 1
> ShowCADLayer[50] = 1
> ShowCADLayer[51] = 1
> ShowCADLayer[52] = 1
> ShowCADLayer[53] = 1
> ShowCADLayer[54] = 1
> ShowCADLayer[55] = 1
> ShowCADLayer[56] = 1
> ShowCADLayer[57] = 1
> ShowCADLayer[58] = 1
> ShowCADLayer[59] = 1
> ShowCADLayer[60] = 1
> ShowCADLayer[61] = 0
> ShowCADLayer[62] = 1
> ShowCADLayer[63] = 1
> ShowCADLayer[64] = 1
> ShowCADLayer[65] = 1
> ShowCADLayer[66] = 1
> ShowCADLayer[67] = 1
> ShowCADLayer[68] = 1
> ShowCADLayer[69] = 1
> ShowCADLayer[70] = 1
> ShowCADLayer[71] = 1
> ShowCADLayer[72] = 0
> ShowCADLayer[73] = 1
> ShowCADLayer[74] = 1
> ShowCADLayer[75] = 1
> ShowCADLayer[76] = 1
> ShowCADLayer[77] = 1
> ShowCADLayer[78] = 1
> ShowCADLayer[79] = 1
> ShowCADLayer[80] = 1
> ShowCADLayer[81] = 1
> ShowCADLayer[82] = 1
> ShowCADLayer[83] = 1
> CADFileComp = "3022.AS10_rcp - DWG"
> ..
>
> CADFile "3022.AS10_base - DWG"
> FileName = "DWGs\3022.AS10_base.dwg"
> FilePathOffset = 3
> ScaleUnits = 0
> ScaleValue = 1
> OriginX = -431.854
> OriginY = -202.058
> Azimuth = 0
> ..
>
> CADFile "3022.AS10_rcp - DWG"
> FileName = "DWGs\3022.AS10_rcp.dwg"
> FilePathOffset = 3
> ScaleUnits = 0
> ScaleValue = 1
> OriginX = -432.278
> OriginY = -201.587
> Azimuth = 0
> ..
>
> HVACWiz "HVAC System 1"
> ScreenIDArrIdx = 0
> OldFurnAFUEDflt = ( 1, 1 )
> SystemPerWhat[1] = "System per Shell"
> ..
>
> HVACWiz "ERV"
> ScreenIDArrIdx = 1
> ScreenIDArrID = 121
> CoolSource[1] = "No Cooling"
> HVACSysType[1] = "Unit Ventilator (no heating or cooling)"
> OldFurnAFUEDflt = ( 1, 1 )
> ..
>
> DXCWWiz "Water-Cooled DX System"
> ..
>
> WSECWWiz "Wtr-Side Econo System"
> ..
>
> WLHPWiz "WLHP System"
> ..
>
> GSHPWiz "GSHP System"
> ..
>
> PrimWiz "Primary HVAC Plant"
> ..
>
> DHWWiz "DHW Plant"
> ..
>
> FacetColor "By Wall Type"
> FacetType = "Walls"
> ColorOption = "By Wall Type"
> ..
>
> FacetColor "By Construction"
> FacetType = "Walls"
> ColorOption = "By Construction"
> ..
>
> FacetColor "Uniform"
> FacetType = "Windows"
> ColorOption = "Uniform"
> ..
>
> FacetColor "By Glass Type"
> FacetType = "Windows"
> ColorOption = "By Glass Type"
> ..
>
> Light3D "Light3D - Default"
> Type = "Default"
> ..
>
> Light3D "Light3D - User1"
> Type = "User Defined 1"
> ..
>
> Light3D "Light3D - User2"
> Type = "User Defined 2"
> ..
>
> Light3D "Light3D - User3"
> Type = "User Defined 3"
> ..
>
> Light3D "Light3D - User4"
> Type = "User Defined 4"
> ..
>
> Light3D "Light3D - User5"
> Type = "User Defined 5"
> ..
>
>
> END_OF_FILE
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090118/5bc17312/attachment-0002.htm>
More information about the Equest-users
mailing list