[Equest-users] Fan Coil Fan Energy
Robby Oylear
robbyo at rushingco.com
Fri Jan 23 12:27:56 PST 2009
I don't think that's it. The PTHP system uses 600% more fan energy than
the fan coil system. It's 205,000 kWh for the PTHP system and only 28,980
kWh for the FC system.
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com/> rushingco.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Keith
Swartz
Sent: Friday, January 23, 2009 12:22 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fan Coil Fan Energy
Robby,
The PTHP system not only has a fan that recirculates inside air across the
inside coil (evaporator coil when cooling, condenser coil when heating),
but it also has a fan to blow outside air across the outside coil
(condenser when cooling, evaporator when heating). The fan coil has only
the inside fan. Perhaps the program is accounting for the energy for the
outside coil fan, which might explain the 15% additional fan energy.
_____________________
Keith Swartz, P.E., LEED AP
Energy Engineer / Senior Project Manager
Energy Center of Wisconsin
455 Science Drive, Suite 200
Madison, WI 53711
Phone: 608.238.8276 x123
Fax: 608.238.0523
Email: kswartz at ecw.org
Web: www.ecw.org
Energy Center University
Your gateway to sustainable design training and online education programs.
<http://www.ecw.org/university/> www.ecw.org/university/
_____
From: Robby Oylear [mailto:robbyo at rushingco.com]
Sent: Friday, January 23, 2009 12:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan Coil Fan Energy
I'm comparing two systems one is a 4-pipe fan coil system and one is a
PTHP system. All of the savings between the two runs seem to make sense
except for a large difference in fan energy between the two. I don't have
detailed product information on the actual fan energy so I currently have
the same kW/CFM value input for both systems. The fan energy of the fan
coil system is 85% less than the PTHP system.
I believe the problem lies with the fan coil system, because it doesn't
have an option available for "Fan Control". I have the Indoor Fan Mode
set to Intermittent, which is how I believe the system would actually
operate since ventilation air is being delivered from a whole house fan.
Can anyone explain to me how the FC system calculates fan power? Why is
there no ability to change the fan control option?
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com> rushingco.com
Logo_B&W_1
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090123/998aecf5/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1804 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090123/998aecf5/attachment-0002.jpeg>
More information about the Equest-users
mailing list