[Equest-users] Occupancy Lighting Sensor

YinRic cesseric at hotmail.com
Wed Jul 1 07:41:30 PDT 2009


Thanks Nick, very helpful! It is indeed a LEED project...I will have a closer look at Table G3.2. Your comments on how to model more accurately is also valuable. 

 

Rick
 


Subject: RE: [Equest-users] Occupancy Lighting Sensor
Date: Wed, 1 Jul 2009 09:10:48 -0500
From: ncaton at smithboucher.com
To: cesseric at hotmail.com









If you are looking at a LEED project, ASHRAE 90.1 dictates what percentage credit (from your lighting power densities) you can take for occupancy sensors, based on what type of occupancy you have, in Table G3.2.  
 
If you are looking to model more accurately (?) based on your project’s unique spatial occupancy patterns and switching configurations with the occupancy sensors (outside of a LEED project), then I believe you can create a custom schedule in eQuest for your lighting loads, adjusting the percentage of the maximum load hour by hour.  
 
~Nick
 

NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 




From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of YinRic
Sent: Wednesday, July 01, 2009 12:26 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Occupancy Lighting Sensor
 
Hi, 
 
Does anyone know if it is possible to simulate occupancy lighting sensor in eQuest? We have a huge warehouse which is not regularly occupied. Occupancy lighting sensors are incorporated in the design. But I don't know how to simulate this...Maybe adjust the schedule in the design case, different from baseline case? 
 
Any comments are appreciated.
 
Rick
PE, LEEd AP



使用新一代 Windows Live Messenger 轻松交流和共享! 立刻下载!
_________________________________________________________________
上Windows Live 中国首页,下载最新版Messenger!
http://www.windowslive.cn
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090701/4b3bef99/attachment.htm>


More information about the Equest-users mailing list