[Equest-users] Equest help
Vikram Sami
VSami at lasarchitect.com
Tue Jul 21 10:11:47 PDT 2009
One thing you need to watch out for is the roofs. Typically if you have
built two shells in the wizard, they will both have roof surfaces and
will be calculating heat transfer through them. When you do move the
shells to be vertically aligned, make sure you:
1. Remove roof surfaces from the lower shell, except where there
is actually exposed roof surface
2. Remove exterior floor surfaces (earth contact or otherwise)
from the upper shell - except where there is exposed floor.
3. Create an internal surface between the spaces - can be defined
on either one of the floors with the other floor defined as the adjacent
zone.
Hope this helps
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Larry
Yang
Sent: Tuesday, July 21, 2009 12:03 PM
To: Lawrence Lee; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Equest help
It's in your basic building shell geometry specifications popup. You can
easily change the 'Z' coordinate position of the floor up on the top of
others and vice visa. Hope it will help.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Lawrence Lee
Sent: July 21, 2009 9:28 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Equest help
Hi all,
I'd like to know if there's a way to move 2 building shells on top of
each other without having to do it in wizard. Is there a command such
as 'move' to place one building shell on top of another? Thanks in
advance.
Lawrence Lee
Mechanical EIT
CROSSEY ENGINEERING LTD.
2255 Sheppard Avenue East Suite E-331
Toronto, Ontario, M2J 4Y1
Phone: (416) 497-3111 ext. Fax: (416) 497-7210
Email: lawrence.lee at cel.ca Web: www.cel.ca
**NOTICE OF CONFIDENTIALITY**
NOTE: This e-mail message is intended only for the named recipient(s)
above and may contain information that is privileged and/or
confidential. If you have received this message in error, or are not the
named recipient(s), please immediately notify the sender and delete this
e-mail message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090721/314eaa5f/attachment-0002.htm>
More information about the Equest-users
mailing list