[Equest-users] PSZ-HP High heating unmet load hours
Seth P. Spangler
sspangle at rmf.com
Mon Jun 15 14:11:13 PDT 2009
Whenever I have multiple zones served by a single zone AHU this is what I do:
In Detailed Edit -->"Air-Side HVAC" tab--> Select a space--> "Spreadsheet" Tab --> restore to default (right click) any zones that are not the control zone in the "Heat Temp and Cool Temp Schedule" columns. You can also set one zone to be the Cool Temp control zone and another to be the Heat Temp control zone. This eliminates the issue when the zone with the highest cooling demand has the lowest heating demand and vice versa.
Hope this helps!
Seth Spangler, EIT, LEED® AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Monday, June 15, 2009 4:59 PM
To: Lam, Linda; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] PSZ-HP High heating unmet load hours
Linda,
Try changing your control zone to different zones to reduce your underheated and undercooled hours. Instead of zones not getting enough heat, it could be that they are getting overcooled. Check your SS-R and SS-O reports. You might also need to adjust supply flow in specific zones instead of on a system-wide basis.
Bill
William Bishop, EIT, LEED® AP | Pathfinder Engineers LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Monday, June 15, 2009 4:30 PM
To: Lam, Linda; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] PSZ-HP High heating unmet load hours
You might want to look at your night cycle fan control:
NIGHT-CYCLE-CTRL
Takes a code-word that specifies whether the fans will cycle on at night or on weekends (implied by a 0 in FAN-SCHEDULE) to maintain the temperature setpoint. The fans are off when the hourly values in the schedule that is referenced by FAN-SCHEDULE are equal to 0. If the hourly schedule values are positive, the fans are on and if the hourly schedule values are negative, the fans are not permitted to be on under any circumstances. NIGHT-CYCLE-CTRL also cycles fans on when the temperature goes above the throttling range of the ZONE:COOL-TEMP-SCH. To lock out this feature you must input a -1 in the FAN-SCHEDULE for the summer (cooling) period. NIGHT-CYCLE-CTRL only affects the fan operation. Once the fans have cycled on, the availability of heating or cooling is controlled by HEATING-SCHEDULE and COOLING-SCHEDULE. Allowed values of NIGHT-CYCLE-CTRL are:
STAY-OFF The fans stay off regardless of conditions.
CYCLE-ON-ANY The fans are cycled on for the hour if the temperature of any zone in the system falls below the throttling range for heating,
CYCLE-ON-FIRST The fans are cycled on for the hour if the temperature in the system's control zone falls below the throttling range for heating.
ZONE-FANS-ONLY For a PIU system, the main or central system PIU fan will remain off but the individual zone terminal fans will cycle on separately to satisfy the heating setback temperature for each zone.
The default is to stay off. It sound like in your situation you want it to cycle on any.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
Please visit our new website | www.lordaecksargent.com <file:///\\www.lordaecksargent.com\>
P Think GREEN before you print.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lam, Linda
Sent: Monday, June 15, 2009 3:09 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] PSZ-HP High heating unmet load hours
Equest Users:
I'm modeling a single story building with 2 packaged rooftop HP units in Las Vegas. I have allowed the program to autosize airflow and cooling and heating capacities.
I'm guessing that the high amount of underheated hours is due to the fact that the PSZ system type uses only one of its assigned zones as the control for constant volume airflow. I have designated the control zone as the zone with the highest internal loads. This works OK in cooling mode, though, I still have about 400 undercooled hours. But in heating mode, the zone with the highest internal loads does not need as much heat as the other zones. Since it's a constant volume system and the control zone is saying "no heat needed", the rest of the zones are not getting any heat. Is that right??
Following through with the assumption above, I tried to increase the minimum cfm/sqft on zone level to 0.5, but my underheated hours went up.
I only manage to decrease unmet heating hours after I increase the cfm on the system level to about 5 times what Trane sizes.
Can someone help me out here?
Thank you!!
Linda
Linda Lam, LEED® AP
WSP Flack + Kurtz
405 Howard Street, Suite 500
San Francisco, CA 94105
Direct: 415.402.5813
Main Tel: 415.398.3833
Fax: 415.433.5311
website: http://www.wspfk.com
vCard: http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf
image: <http://vcards.wspfk.com/usercard.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.png>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090615/149db1b2/attachment-0001.htm>
More information about the Equest-users
mailing list