[Equest-users] Munters Unit
Drake.Wahlers at tac.com
Drake.Wahlers at tac.com
Fri Jun 12 11:34:33 PDT 2009
Karen,
If your trying to approximate the energy use of a Dry Cool Munters Unit
versus a regular unit, in a parametric run, first specify 100% for
maximum humidity control.
You must then adjust your cooling capacity. Remember that a Munters Unit
doesn't need to "over-cool". You could approximate this using a
psychometric chart. Figure out the difference in enthalpy between your
mixed air condition and your coil discharge condition (accounting for
over-cooling) for a regular unit. Then figure out the enthalpy
difference for your Munters unit, which would be your mixed air
condition and your desired supply air condition (55F, 50%RH for
example). The ratio between those differences should give you a good
approximation on how much to de-rate your cooling capacity.
-Drake
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen
Walkerman
Sent: Thursday, June 11, 2009 10:27 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Munters Unit
Has anyone modeled (or approximated) a munters unit in eQuest? Any
suggestions on how this could be done?
Thanks,
--
Karen