[Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors
cic at jci.com
cic at jci.com
Wed Jun 17 20:23:05 PDT 2009
Evans/Ashu,
Thanks for the reply,
I want to keep the user feed U-value. In that case, is it acceptable if we
ignore the error message ?. or else what needs to be done to take care of
both the aspect (user value + no error message).
Please provide your inputs.
Also I am getting the following two more errors. Pls provide your inputs
as well.
MULTIPLIER in EL1 Core Zn (G.C80) has Expression Evaluation Error: Invalid
BDL reference
Line 17483: Thermal Zone: EL1 Core Pl Zn (G.C160)
Line 17489: Error Encountered:
EL1 Core Plnm (G.C81) was referenced on line 2143 but never defined.
(lLineNum = 1000000)
Line 17545: Error Encountered:
Thanks and regards
Kathiresan
Jon Evans <JEvans at sustaineng.com>
Sent by: equest-users-bounces at lists.onebuilding.org
06/17/2009 07:57 PM
To
ashu gupta <kce2 at kamalcogentenergy.com>, "cic at jci.com" <cic at jci.com>
cc
"equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Subject
Re: [Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0
delayed walls, 1 delayed floors
Kathiresan,
Ashu?s approach eliminates the warning.
But, the reason the warning occurs is overriding the layers input for
walls, roof, floor to be a U-value override (user input). The layers input
accounts for the time delay properties of the wall (think of it like a
capacitor) while the U-value override only looks at the steady state heat
transfer.
Thanks.
Jon Evans, PE, LEED AP
Sustainable Engineering Group LLC
431 Charmany Drive Suite 102
Madison, WI 53719
Tel: (608) 231 9664 x 13
Fax: (608) 231 9665
E-mail: jevans at sustaineng.com
Web: www.sustaineng.com
From: ashu gupta [mailto:kce2 at kamalcogentenergy.com]
Sent: Wednesday, June 17, 2009 12:50 AM
To: cic at jci.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39)
has 0 delayed walls, 1 delayed floors and 0 delayed ceilings
Hi Kathiresan,
To eliminate this warning you have to double click on this space and go to
the content option then fill the minimum floor weight =70lb/ft².
Window for your reference
Thanks
Ashu Gupta,
Project Engineer,
Kamal Cogent Energy,
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
cic at jci.com
Sent: Wednesday, June 17, 2009 10:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0
delayed walls, 1 delayed floors and 0 delayed ceilings
Dear All.
I am getting the following warning while running equest, What needs to be
done to eliminate this error in the model?.
SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors and 0
delayed ceilings. There should be at least a delayed wall and floor, a
delayed wall and ceiling, or a delayed ceiling and floor for custom
weighting factors to be calculated. ASHRAE weighting factors with floor
weight of 70 lb/ft2 (342 kg/m2) will be used for this space. (lLineNum =
1000000)
Line 7871: Warning Encountered:
Advance thanks for the help.
Regards,
Kathiresan_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090618/4e4e8a97/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 49262 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090618/4e4e8a97/attachment-0002.jpeg>
More information about the Equest-users
mailing list