[Equest-users] eQUEST - new user
Karen Walkerman
kwalkerman at gmail.com
Wed Mar 11 07:48:38 PDT 2009
Hi Aswan,
1. This depends partly on what the model is for. If this is a LEED model,
the zones should be modeled as designed in the mechanical plan. If it's
not, you may want to simplify further, combining zones with similar uses and
exposures as long as you are pretty confident that the hourly heading and
cooling loads will be similar. Definitely err on the side of simplicity and
whatever you do, don't model closets separately.
2. You can define one AHU that serves multiple spaces, regardless of where
those spaces are. You might have to do some fine-tuning in detailed edit
mode in order to get everything set-up the way you want. There is no
chilled beam in eQuest. You'll have to modify an airside cooling system to
approximate the chilled beam. Search the archives for info on how to do
this. There have been at least a few discussions on the list serve in the
past regarding this issue.
3. It's possible to model CHP systems in detailed mode. Basically, create
an electric generator, select the fuel source and select the heat reject
loops. You can adjust the performance curves to match the type of equipment
you want to model. A word of caution: eQuest does not know the temperature
at which the generator is rejecting heat. Therefore it's possible to model
a generator that rejects heat at 85 F into a loop that needs to be
maintained at 180 F, but this violates the laws of thermodynamics!
--
Karen
On Wed, Mar 11, 2009 at 6:21 AM, Aswan Ali
<aswan.ali at hurleypalmerflatt.com>wrote:
> Hi all,
>
>
>
> I’ve just started creating my first model on eQuest and can really do with
> some advice.
>
>
>
> The project is quite complex and consists of 2 high quality office towers
> and an 8-storey trading and banking building.
>
>
>
> The HVAC systems serving the 3 buildings vary from VAV, chilled beams,
> perimeter trench heating, AHUs with reheat to CHPs.
>
>
>
> I have the following questions please:
>
>
>
> 1. What things should I consider when creating the HVAC zones?
>
>
>
> 1. How should I model the different HVAC systems? For example, when one
> or more AHUs are serving multiple floors, do I define each AHU separately
> and assign them to the various HVAC zones?
>
>
>
> 1. How can I model a combined heat and power (CHP) system?
>
>
>
> Your help is very much appreciated.
>
>
>
> Kind regards,
>
>
>
> *Aswan** Ali**
> Graduate Mechanical Engineer*
>
> *Building Services Division*
>
> * *
>
> *hurleypalmerflatt** *
>
> *building* *sustainability*
>
>
>
> *d:* +44(0) 20 7535 3124
>
> *t:* +44(0) 20 7535 3100
> *f:* +44(0) 20 7535 3101
>
> *e:* aswan.ali at hurleypalmerflatt.com
>
> *w: *www.hurleypalmerflatt.com
>
>
>
> View company email disclaimer at:
> http://owa.hurleypalmerflatt.com/disclaimer.asp
>
> * *
>
> *P* *Please consider the environment before printing this email**.*
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090311/10db8ed1/attachment-0001.htm>
More information about the Equest-users
mailing list