[Equest-users] Number of heating hours not met
David Dowling
David.Dowling at WestPlainsEngineering.com
Wed May 13 06:46:15 PDT 2009
I am using the ASHRAE 90.1-2004 compliant system number 3 which happens
to be DX Coils with Furnace.
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com <http://www.westplainsengineering.com/>
________________________________
From: Charles Land [mailto:cland at geo-marine.com]
Sent: Wednesday, May 13, 2009 6:12 AM
To: David Dowling; equest-users at lists.onebuilding.org
Subject: RE: Number of heating hours not met
What type of systems are you using?
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Tuesday, May 12, 2009 6:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Number of heating hours not met
I have a question concerning a warning related to the number of heating
hours not met and apologize in advance if this topic has been covered
before. The warning I am getting is:
"Zone might have insufficient heating capability. Check that the system
or zone HEATING-CAPACITY plus this zones BASEBOARD-RATING is adequate to
maintain the zone specified DESIGN-HEAT-T for the calculated peek zone
load (see LS-A or LS-B for the zone peak load)."
I am using the auto sizing function within eQuest so I am not
understanding why the spaces are not satisfied. Dose anyone know how to
make the auto size function work to satisfy each zone?
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com <http://www.westplainsengineering.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090513/761bf118/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4427 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090513/761bf118/attachment-0001.jpeg>
More information about the Equest-users
mailing list