[Equest-users] Modeling Window changes

Matutinovic, Luka LMatutinovic at halsall.com
Fri May 29 07:29:09 PDT 2009


John,
 
It's difficult to diagnose your issue without having the .inp and .pd2
files to review.  
 
What do you mean by "more energy efficient"?  If you are referring to
U-value, the result does seem counter-intuitive (unless the negative
result is actually a reduction in energy shown as a "negative").  If
however, you consider a reduction in the SHGC to be more energy
efficient, this may in fact lead to increased energy use in heating
dominated climates since less solar gain is available in the winter.  As
I said, seeing the simulation would be helpful.
 
Cheers,

Luka Matutinovic, B.A.Sc., LEED(r) AP

Green Building Consultant
 
T. 416.487.5257 ext. 317  
F. 416.487.9766  
Toll Free 1.888.425.7255
www.halsall.com 

HALSALL ASSOCIATES LTD. 
Toronto  Richmond Hill  Ottawa  Sudbury 
Burlington  Calgary  Vancouver  Dubai 

'Best Workplaces in Canada' 
2009 Globe and Mail
P Please consider the environment before printing this e-mail


________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
jklikape at aol.com
Sent: Friday, May 29, 2009 10:23 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Window changes


Good Morning,
My associate and I are beginners on the E-Quest program and are feeling
our way around the program.  Among many other questions that we may have
we are in a quandry as to why, when we use a more energy efficient
window in the EEM module, the results show a negative effect in our
simulation.  Is there some basic fundimental we,re missing here? 

John Klika
KGZ Consulting Engineers, Ltd.
Joliet, Illinois 
815-714-2818 

________________________________

Wanna slim down for summer? Go to America Takes it Off
<http://www.aolhealth.com/diet/weight-loss-program/?ncid=emlcntusheal000
00001>  to learn how. 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090529/bdfce3f8/attachment-0001.htm>


More information about the Equest-users mailing list