[Equest-users] Hours outside Thrl-Range
eric wang
shaojieworld2006 at yahoo.com
Wed May 27 13:38:01 PDT 2009
David,
If several zones have the unmet hour at the same time, it is counted as one unmet hour instead of several unmet hours for each zone. DOE-2 report SS-F shows the unmet hours for each zone.
I hope this will help
Shaojie
--- On Wed, 5/27/09, David Dowling <David.Dowling at WestPlainsEngineering.com> wrote:
From: David Dowling <David.Dowling at WestPlainsEngineering.com>
Subject: [Equest-users] Hours outside Thrl-Range
To: equest-users at lists.onebuilding.org
Date: Wednesday, May 27, 2009, 3:58 PM
Does any one know how the “PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE” from detailed output BEPS is calculated? I am assuming it is the maximum total number of ours any given system zone is not within the throttling range divided by 8760. If this is true, why can’t I seem to find the total number of hours from any of the reports to give me this percentage? Any information concerning this is greatly appreciated.
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com
-----Inline Attachment Follows-----
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090527/80e38798/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4427 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090527/80e38798/attachment-0002.jpeg>
More information about the Equest-users
mailing list