I think you've identified the root of your problem - I'm unsure that
there's any way to get light in one shell to transmit to another.

 

Attached and below is an example of a project with a lot of roof
monitors that does successfully measure and account for daylighting in
those spaces.  A  picture speaks a thousand words, so see if this
matches what you were thinking to accomplish.  

 

Each monitor is a single zone and shell (i.e. no plenum zone).  Sensors
are located either on the floor or at a desk height, as appropriate to
the space usage.  Creating the shell that "wraps" around the monitors is
done by using "cutting lines" in the footprint/zoning pattern - you can
read up on that strategy by searching the archives for how courtyards
are modeled.  

 

I'll point out, in terms of accuracy, I have the impression that
eQuest's daylight sensors do not accurately realize the full amount of
light that should be encountered with light shelves, light tubes, or
other means of interreflected daylight, based on my comparative daylight
analyses using AGI32 (which I've learned to use accurately for daylight
modeling).  The DOE2 help files I think also allude to this - It's
something to keep in mind if you have a lot of monitor overhangs, again
as with the example below.

 

~Nick

 

 

 

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Smith,
Aaron Matthew
Sent: Thursday, November 19, 2009 9:42 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Roof monitor "Open to Below"

 

Hello E-quest group,

 

I am working on ways to implement Equest in my workflow for the purpose
of daylighting design evaluation, and I am having trouble implementing a
roof monitor. I have read the help files that describe the limitations
of Equest to perform daylighting calculations, but I have also seen that
some people have been able to implement multilevel atriums and I have
seen one application of a roof monitor. Anyways I want to give it a go
before I start programming in Daylight Factors.  

 

Attached is an example building I would like to be able to evaluate. My
evaluation goal is to put a light meter on the bottom zone under the
monitor and see what results pop out in the detailed daylighting summary
reports (LS-G, LS-J, ect.) I would like to compare Equest results to the
results of other software/calculations/measurements I am investigating,
however it seems that no light from the roof monitor is making it to the
bottom zone.

 

The bottom shell is all one zone and the top is all one zone. I have
found that it is necessary that the bottom zone have windows or else no
daylighting dialog screen shows up in the DD wizard, and that means no
light meter. At first I tried to make the top zone "open to below" and
then in the detailed edit mode moved the light meter under the monitor,
but the results do not indicate any light is making it from the roof
monitor to the bottom zone.

 

I was hoping some of you might have some suggestions to help implement
this roof monitor setup.

 

Thanks,

Aaron

 

Aaron Smith

Sr. Research Specialist

smitha11 at rpi.edu

 

Lighting Research Center

21 Union Street

Troy, NY 12180

p. 518.687.7167

f.  518.687.7120

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091119/334deee5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091119/334deee5/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 529962 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091119/334deee5/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3D Model View.JPG
Type: image/jpeg
Size: 81969 bytes
Desc: 3D Model View.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091119/334deee5/attachment-0001.jpeg>


More information about the Equest-users mailing list