[Equest-users] System Reports

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Wed Nov 4 09:57:11 PST 2009


Oleksandra,

This might help explain things:

SV-A - System Design Parameters
This report is based on your inputs to the program for the selected Systems
(in your case PVVT.)

Cooling Capacity & Heating Capacity values reported is either the value that
you entered for your inputs at the system level, or it is computed by the
SYSTEMS program from the peak cooling load.  (Peak = Sens + Lat)  If the
capacity is input at the zone level then the value reported at the system
level (top of report) will be zero.

SS-A - System Monthly *Loads* Summary
The loads shown in this report are the *sum* of zone-level loads and the
central air-handling-unit loads.  Zone level loads are not shown in this
report.  This report is good for comparing monthly heating and cooling *needs
*of the HVAC system (needs is the key word here, because it what the 'rooms
are calling for' to the system to provide.)  The DX cooling loads for your
PVVT system are reported in this report but these loads do not get passed on
to the PLANT program.

To answer your question you cannot compare the two reports to be equal,
because one reports capacity values and the other (SS-A) reports load
values.  Capacity and loads are two different things.  The two reports you
are looking at should be used in support of each other for verification of
your model, not in comparison to each other.  As far as your issue with the
heating and cooling capacity being reported equal to each other in SV-A
report, this is probably based on what you input for your equipment
capacities.

if you have more questions feel free to contact me.

Pasha

On Wed, Nov 4, 2009 at 9:22 AM, Oleksandra Onisko <OOnisko at mcw.com> wrote:

>  Hi All,
>
>
>
> I am looking at the simulation output reports, specifically at the SS-A:
> System Loads Summary and SV-A System Design Parameters.  The peak heating
> and cooling loads are shown in the SS-A report and the system capacities are
> shown in the SV-A report. The SV-A report shows the heating capacity being
> equal to the cooling capacity which does not match the SS-A report and does
> not seems right.  Any ideas about this? I am looking at PVVT systems.
>
>
>
> Thanks,
>
>
>
> *Oleksandra Onisko* LEED AP
>
> *EIT*
>
>
>
> *MCW Consultants Ltd. * <http://www.mcw.com/>
>
> *600-156 Front Street** West
> Toronto, ON M5J 2L6** **
> Phone 416-598-2920
> Fax 416-598-5394 *
>
>
>
> *This e-mail may be privileged and confidential. Any unauthorized use is
> strictly prohibited. If you received this e-mail in error, please contact
> the sender directly. *
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091104/ccc7ecde/attachment-0002.htm>


More information about the Equest-users mailing list