[Equest-users] HVAC Loads Based on eQuest
Crockett, Jim
Jcrockett at nexant.com
Thu Nov 5 08:39:01 PST 2009
If you're just designing offices, strip malls, churches, etc., then the
Trane program is much, much quicker, and any difference in accuracy is
smaller than the uncertainty embedded in your assumptions. (e.g., will
the customer add more equipment, leave the door open, keep the blinds
open, etc.)
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Hernandez, Arturo
Sent: Thursday, November 05, 2009 9:27 AM
To: James Hess; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] HVAC Loads Based on eQuest
I guess the problem is when calculating loads you may want to be a
little more conservative with you internal loads and when you are doing
energy modeling you want to be more exact with your assumptions. In
addition, my understanding is that internal loads contribute to space
heating in eQuest load calcs. Which something that many engineers would
not feel comfortable with.
ARTURO HERNANDEZ, Mechanical Engineering
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James
Hess
Sent: Thursday, November 05, 2009 10:03 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] HVAC Loads Based on eQuest
That's the way are offices typically do it as well (i.e. Trace for
loads, eQuest for energy).
I have found that when both programs use the same inputs for envelope,
lighting, misc equipment, etc., the two programs produce results that
are pretty close.
Regards,
James A. Hess, PE, CEM
Energy Engineer
TME, Inc.
Little Rock, AR
ph 501-666-6776
cell 501-351-4667
jhess at tmecorp.com <mailto:email at tmecorp.com>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Hernandez, Arturo
Sent: Thursday, November 05, 2009 9:13 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC Loads Based on eQuest
Just wondering... Has anyone based their HVAC design on eQuest results?
Typically we us Trane Trace for load calcs and do our energy models in
eQuest. However, this questions was brought up in our office. I just
wanted to see what everyone thought of this matter.
Arturo Hernandez