When you build a project in eQuest using the wizard, the HDD schedules are
set to 0 for all internal loads.
When eQuest auto-sizes, it uses the weather file data and takes solar gain
into account for both heating and cooling, if you need any. You can create
custom heating and cooling design days that specify the hour at which the
high and low temperature is reached. For a heating design day, the hour low
could be specified to be at night, when there is no solar gain. Also, in
LS-B and LS-C reports, the solar gain is clearly called out, if there is any
solar gain during the heating design day, it cab be subtracted out of the
total load for the space.
Thanks,
--
Karen Walkerman
Second Law
802-238-0980
karen at secondlaw.biz
On Thu, Nov 5, 2009 at 12:51 PM, Hernandez, Arturo <ahernandez at owpp.com>wrote:
> Last thing I would like to bring up on this topic: Is solar heat gain
> taken as a credit during your HDD and if so how could this be “shut-off”.
>
>
>
> *ARTURO HERNANDEZ, Mechanical Engineering*
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *David S
> Eldridge
> *Sent:* Thursday, November 05, 2009 10:46 AM
> *To:* equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] HVAC Loads Based on eQuest
>
>
>
> I think there is another question about how detailed your load calculation
> will be in breaking down the building compared to the resolution required
> for your energy model, but you might be able to navigate the differences
> successfully. And for some projects there may not be much difference.
>
>
>
> Also whether the same person is doing both tasks, and their familiarity
> with both software packages. Arturo, if you were doing both then great, but
> what if you have to hand the load calc tasks off to someone at your office
> that doesn’t use eQuest?
>
>
>
> David
>
> http://www.grummanbutkus.com
>
>
>
>
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Hernandez,
> Arturo
> *Sent:* Thursday, November 05, 2009 10:41 AM
> *To:* Howe, Timothy; James Hess; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] HVAC Loads Based on eQuest
>
>
>
> You are correct. Therefore one would just have to schedule that to be off
> all the time in HDD. So are there any other any concerns with using eQuest?
> Is the answer simply: It is easier to get the load calculations from Trane
> Trace?
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091105/a58bd1f2/attachment-0002.htm>
More information about the Equest-users
mailing list