[Equest-users] Floor Alignment Problem
Nick Caton
ncaton at smithboucher.com
Mon Nov 23 14:50:30 PST 2009
Regarding alignment of shells in three dimensions, my practice is
personally to try and nail this potential issue down within the wizards,
before the detailed mode. To do so, I avoid "immediately above" or any
of the other myriad of similar options like the plague when defining
each shell. I always position "via coordinates," and set each shell to
be X=0, Y=0, Z="whathaveyou." This does hinge around having CAD
references which all share the same X/Y origin (normal practice in our
office to begin with for clean xref's during drafting), and a little
extra thought to ensure my "floor-to-floor" heights defined on the
second screen add up correctly to each Z-elevation I define for shells.
The end result however is I don't need to concern myself with
mis-alignment issues - this allows me to lean confidently on the
shared-plane recognition Scott Criswell defined nicely in an email
response this morning to the subject (RE: [Equest-users] Roof monitor
"Open to Below").
To address your last two questions, I'd again refer you to the same
email from Scott where he outlined how shells' floors/roofs should be
handled when stacked on top of each other. You will want to, in
detailed mode after the wizards, change the shared roof/floor areas of
each shell into non-exterior constructions.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Nicholas Couture, LEED AP
Sent: Monday, November 23, 2009 11:26 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Floor Alignment Problem
Hello,
I'm modeling a two-story building with basement and penthouse and am
having a slight problem (maybe??). First I modeled the shells (one per
floor) and checked "immediately above" each other without specifying
coordinates. The floor alignment was not correct (all floors were
centered with respect to each other) even though I used the background
of the floor below as a reference. To try to fix this I left the
basement as it was without specific coordinates and plugged in
coordinates for the 1st Fl, 2nd Fl, and penthouse. Now the 1st Fl, 2nd
Fl, and penthouse are aligned correctly with respect to each other, but
the basement is not aligned in the 3d view (see below). The basement
appears to be aligned with the 1st floor in the custom building
footprint (see below), so there seems to be a conflict.
Can someone help me align these, and get rid of the floor heat transfer
between the basement and the 1st floor?
Also since I created multiple shells for each floor, do I need to go
into detailed edit mode and delete the underground floor components of
the upper levels?
Also any advanced procedures for what I did above would be beneficial?
thanks,
Nick Couture, LEED AP
Jr. Mechanical Engineer
3555 Veteran's Memorial Highway, Suite M
Ronkonkoma, NY 11779
Tel: 631.981.3990 ext. 230
Fax: 631.981.3971
ncouture at emtec-engineers.com
www.emtec-engineers.com <http://www.emtec-engineers.com/>
This message is intended only for the personal and confidential use of
the designated recipient(s) named above. This is not in anyway an
official statement of Emtec Consultants or solicitation to buy our
services. Emtec Consultants does not guarantee this Email transmission
to be secure or error-free. Any reproduction or changes to our drawings
and files without the consent of Emtec Consultants is strictly
prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091123/7478e3c1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091123/7478e3c1/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 182323 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091123/7478e3c1/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 411988 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091123/7478e3c1/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 26315 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091123/7478e3c1/attachment-0011.jpeg>
More information about the Equest-users
mailing list