[Equest-users] eQUEST: Heat Recovery Chiller
    Tony Kriel 
    TKriel at sustaineng.com
       
    Tue Oct  6 06:33:44 PDT 2009
    
    
  
If I were to setup another heat recovery chiller I would use the following steps.  If anyone would like to add some comments or some additional steps, please feel free to do so.
1.       Assumptions: You're in detailed mode, and you have a water cooled chiller setup with a chilled water loop, condenser water loop, and a hot water loop.
2.       Create a new chiller. Type = Elec Heat Recovery
3.       Assign loops. CHW = Chilled Water Loop, CW = Condenser Water Loop, HtRec = Hot Water Loop.
4.       Verify/input the EIR, equipment capacity, whether the chiller is at Design or Rated conditions.
5.       Change the chilled water temperature, condenser temperature, min condenser temperature, and maximum het recovery setpoints if necessary.
6.       Create/change EIR and Capacity curves if necessary.
Regards,
Tony Kriel
________________________________
From: Otto Schwieterman [mailto:oschwieterman at fhai.com]
Sent: Tuesday, October 06, 2009 8:17 AM
To: Tony Kriel; equest-users at lists.onebuilding.org.
Subject: eQUEST: Heat Recovery Chiller
Tony, have you figured out or received a step-by-step process for simulating a heat recovery system?
Thanks, Otto
______________________________________________________________________________
Tony-
When you define a chiller in eQuest, along with assigning the appropriate
CHW (and possibly CW and HW) there is also a loop assignment for "HtRec".
This takes either a HW, WLHP, or DHW Loop to which the chiller will attempt
to provide recovered heat to.  There are some variables you will need to
fill in depending on how much heat you want to recover, etc...
If that doesn't answer your question, please let me know.
Regards,
--
Steve Mignogna
Atelier Ten
On Mon, Mar 9, 2009 at 4:55 PM, Tony Kriel <tkriel at sustaineng.com<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>> wrote:
>  I know this has been asked once or twice before, but I haven't had too
> much luck finding an appropriate archived response.
>
>
>
> Has anyone successfully modeled a heat recovery chiller in Equest that
> would reject heat to a domestic hot water loop and would like to share a
> step by step process for simulating such a system?
>
>
>
> Thanks,
>
>
>
> Tony Kriel, LEED AP
>
> Mechanical Engineer
>
> tkriel at sustaineng.com<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
>
> (608) 231-9664 ext. 16
>
>
>
> Sustainable Engineering Group, LLC.
>
> 431 Charmany Drive, Suite 102
>
> Madison, WI 53719
>
> www.sustaineng.com
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity.   If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful.   Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091006/bdc6584c/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list