[Equest-users] DHW in the DD Wizard - question
    Umesh Atre 
    umesh at innovativedesign.net
       
    Tue Oct  6 14:30:19 PDT 2009
    
    
  
 
Mike,
 
The laundry facilities inputs show up only if your building type is
'Multifamily', which seems like you have.
The DHW Equipment tab/menu on the Project Navigator screen is tied to
the 'Non-HVAC Enduses to Model' screen. Please make 
sure you have checked the 'Domestic Hot Water' on this screen. Hope this
helps.
 
 
 
 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike
Diess
Sent: Tuesday, October 06, 2009 3:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DHW in the DD Wizard - question
I am modeling multi-family builings with individual washing machines.
When I input a multi-family bldg. I initially got a DHW menu in the
project navigator. That option has now greyed out & I cannot get it
back. Does anyone know what triggers the activation of the DHW menu in
the project navigator?
thanks Mike
-- 
Mike Diess, PE, LEED AP
LNI Consulting Engineering  
mike.diess at gmail.com
cell: 720-427-7954   fax: 608-646-1063
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091006/d92454b2/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list