[Equest-users] outside air ratio
Verena Kindl
kindl at scholze.de
Fri Sep 11 06:13:03 PDT 2009
Thank you, but i already thought about that and i have nothing specified
there. But now I tried to specify the flow to each zone instead of doing
it for the whole system and then the outdoor air ratio is calculated
correctly. Of course I considered the induction ratio so I specified for
each zone 1962 cfm supply flow (induction ratio of 2) then I get an
outdoor air ratio of 1 and 918 cfm OA per zone. Do you think I can do
that? It is strange so as the other way should work as well.
________________________________
Von: Bouchard, Jordan [mailto:Jordan.Bouchard at stantec.com]
Gesendet: Freitag, 11. September 2009 15:08
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: [Equest-users] outside air ratio
Hi Verena,
Check your zone level OA values. If you want to specify 100% OA at the
system level you have to clear the zone level inputs as they will
override the system level OA inputs.
Regards,
Jordan Bouchard, LEED(r) AP
Mechanical Engineer In Training
Stantec Consulting Ltd.
Ph: (416) 596-6686
Fx: (416) 596-6680
Jordan.Bouchard at stantec.com
stantec.com <http://www.stantec.com>
The content of this email is the confidential property of Stantec and
should not be copied, modified, retransmitted, or used for any purpose
except with Stantec's written authorization. If you are not the intended
recipient, please delete all copies and notify us immediately.
* Please consider the environment before printing this email.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena
Kindl
Sent: Friday, September 11, 2009 8:57 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] outside air ratio
Hi all,
I have an induction unit for the whole building, supplying 204000 cfm
outside air to the building. So I specify the supply flow of the system
(204000 cfm) and set the min outside air ratio =1. In the SV-A report it
shows on the system level 0 outside air and therefore no cooling/heating
capacity and for the zone it shows about 800-1100 cfm outside air. Only
if I do not specify the supply flow on the system level then I also get
an outside air ratio of 1 for the system level. Why is it not possible
to tell equest that the 204000 cfm it supplies is only outside air. I
have not specified an economizer so it should be outside air all the
time ??
Have a nice weekend.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090911/d9465d73/attachment-0001.htm>
More information about the Equest-users
mailing list