[Equest-users] General Advice
Lars Fetzek
lfetzek at phoenixeng.us
Mon Sep 14 14:12:06 PDT 2009
eQuesters,
I have solved my problem, described below (from previous e-mails). My
solution leads me to send the following advice to everyone:
Be aware that adding comments (i.e. text preceded by a dollar sign) in a
.inp file, even at the end of an already functional line of code, can cause
mysterious problems in eQuest's interpretation of other (seemingly
unrelated) lines of code.
Lars Fetzek, EI
Phoenix Engnineering Group
Tampa, Florida
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lars Fetzek
Sent: Monday, September 14, 2009 4:04 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Error question
eQuesters & Brett,
Thanks for your help, Brett. The BDL file shows the following. It also
showed the same error with or without quotes around the U-name in line 3017
and with or without the $ in line 3010. Evidently, eQuest is just not
recognizing the parent system that I defined line lines 2994 - 3016.
Does anyone know why this would be - especially when, as explained in
the original e-mail (below), I based this code on that generated by eQuest?
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
*2988 * $ *********************************************************
*2989 * $ ** **
*2990 * $ ** HVAC Systems / Zones **
*2991 * $ ** **
*2992 * $ *********************************************************
*2993 *
*2994 * "HVAC1 System" = SYSTEM
*2995 * TYPE = PVAVS
*2996 * HEAT-SOURCE = NONE
*2997 * ZONE-HEAT-SOURCE = ELECTRIC
*2998 * BASEBOARD-SOURCE = NONE
*2999 * SIZING-RATIO = 1.15
*3000 * MAX-SUPPLY-T = 95
*3001 * MIN-SUPPLY-T = 55
*3002 * ECONO-LIMIT-T = 65
*3003 * ECONO-LOCKOUT = YES
*3004 * OA-CONTROL = FIXED
*3005 * FAN-SCHEDULE = "HVAC1 Fan Sch"
*3006 * FAN-CONTROL = FAN-EIR-FPLR
*3007 * SUPPLY-STATIC = 3.569
*3008 * SUPPLY-EFF = 0.521452
*3009 * RETURN-EFF = 0.53
*3010 * $ FAN-EIR-FPLR = "Variable Speed Drive FPLR"
*3011 * REHEAT-DELTA-T = 15
*3012 * COOLING-CAPACITY = 379900
*3013 * COOLING-EIR = 0.324232
*3014 * CRANKCASE-HEAT = 0
*3015 * FURNACE-HIR = 1.24067
*3016 * ..
*3017 * Zone-Space-1A = ZONE
*ERROR**********************************************************************
******************
*ERROR*****A PARENT SYSTEM must be defined before you can define this ZONE
*3018 * TYPE = CONDITIONED
*3019 * MIN-FLOW-RATIO = 0.3
*3020 * FLOW/AREA = 0.5
*3021 * OA-FLOW/PER = 155.325
*3022 * EXHAUST-FLOW = 1130
*3023 * EXHAUST-STATIC = 0.75
*3024 * EXHAUST-EFF = 0.411758
*3025 * DESIGN-HEAT-T = 68
*3026 * HEAT-TEMP-SCH = "HVAC1 Heat Sch"
*3027 * DESIGN-COOL-T = 76
*3028 * COOL-TEMP-SCH = "HVAC1 Cool Sch"
*3029 * SIZING-OPTION = ADJUST-LOADS
*3030 * SPACE = "Space 1A Space"
*3031 * ..
_____
From: Brett Fero [mailto:bfero at robsonwoese.com]
Sent: Monday, September 14, 2009 3:22 PM
To: Lars Fetzek; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Error question
Lars,
My suggestion would be to open the bdl file and search for "error". This
will indicated direct you to where error occurred. Too many errors and
eQuest gives up.
If you are manually editing the inp file, make sure you have two periods
".." at the end of you commands as required.
Brett Fero, P.E., LEED AP
RobsonWoese Inc.
<mailto:bfero at robsonwoese.com> bfero at robsonwoese.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lars Fetzek
Sent: Monday, September 14, 2009 3:08 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Error question
eQuesters,
I included the following text in my .inp file, copied-and-pasted from an
.inp file that eQuest generated. My intention is to edit it to reflect the
conditions of the present project, which I really really don't want to have
to re-create in the wizard, since I've already composed about 3,000 lines of
.inp code for complex geometry, schedules, etc. As of yet, the only thing
that I've edited are the U-names referring to the fan schedule, the heat
schedule, the cool schedule, and the space - so that they match the present
project. Scrolling down in this e-mail, you'll see the lovely error
messages that appear when I load the .inp file into eQuest. Can anyone tell
me what is wrong and how to fix it? (Yes, I clicked on the errors, but
eQuest tells me nothing helpful.)
By the way, my concern here is only with HVAC errors and not with the
electric meter error, which simply results from me having commented-out the
electric meter code in the .inp file.
Thanks if you have advice...
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
$ *********************************************************
$ ** **
$ ** HVAC Systems / Zones **
$ ** **
$ *********************************************************
"HVAC1 System" = SYSTEM
TYPE = PVAVS
HEAT-SOURCE = NONE
ZONE-HEAT-SOURCE = ELECTRIC
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1.15
MAX-SUPPLY-T = 95
MIN-SUPPLY-T = 55
ECONO-LIMIT-T = 65
ECONO-LOCKOUT = YES
OA-CONTROL = FIXED
FAN-SCHEDULE = "HVAC1 Fan Sch"
FAN-CONTROL = FAN-EIR-FPLR
SUPPLY-STATIC = 3.569
SUPPLY-EFF = 0.521452
RETURN-EFF = 0.53
FAN-EIR-FPLR = "Variable Speed Drive FPLR"
REHEAT-DELTA-T = 15
COOLING-CAPACITY = 379900
COOLING-EIR = 0.324232
CRANKCASE-HEAT = 0
FURNACE-HIR = 1.24067
..
"Zone Space 1A" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
OA-FLOW/PER = 155.325
EXHAUST-FLOW = 1130
EXHAUST-STATIC = 0.75
EXHAUST-EFF = 0.411758
DESIGN-HEAT-T = 68
HEAT-TEMP-SCH = "HVAC1 Heat Sch"
DESIGN-COOL-T = 76
COOL-TEMP-SCH = "HVAC1 Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Space 1A Space"
..
________________________________________________________________________
This Email has been scanned for all viruses by PAETEC Email Scanning
Services, utilizing MessageLabs proprietary SkyScan infrastructure. For more
information on a proactive anti-virus service working around the clock,
around the globe, visit http://www.paetec.com.
________________________________________________________________________
_____
"This message is for the designated recipient only and may contain
privileged, proprietary, or otherwise private information. If you are not
the intended recipient, you are hereby notified that any disclosure,
copying, distribution, or the taking of any action in reliance on the
contents of this information is strictly prohibited. If you have received
this transmission in error, please notify the sender immediately by e-mail
and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/01eeafcf/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 161273 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/01eeafcf/attachment-0001.jpeg>
More information about the Equest-users
mailing list