[Equest-users] capacity check
Verena Kindl
kindl at scholze.de
Mon Sep 7 04:23:19 PDT 2009
I am so sorry i thought you were making fun of me. But actually the
units conversion tricked me. I am so sorry.
________________________________
Von: Charles Land [mailto:cland at geo-marine.com]
Gesendet: Freitag, 4. September 2009 19:00
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: capacity check
Try Q=500*gpm*dT
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena
Kindl
Sent: Friday, September 04, 2009 9:11 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] capacity check
Hi equester,
i was checking my results fort he chilled water loop. I entered a delta
T of 11,8 F and a capacity of 21 MBTU/ h and in the PV-A report I find
also 21 MBTU/h and a flow of 3556.5 gpm (593 lb/s). I checked the delta
T using the formula Q=m*c*delta T
Delta T = Q/(m*c)
Delta T = 21*e6 Btu/h / (593 lb/s*3600s/h* 1 Btu/lbF ) = 9,8 F
The mass flow is too high and the delta T too low but i have not
specified a massflow for the loop so it was up to equest sizing the
massflow. Do you get appropriate massflows ? I tried it with other delta
T but the temperature difference is always too low and the massflow to
high. Sizing option is primary. Any idea? Have a nice weekend.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090907/034b87a6/attachment-0002.htm>
More information about the Equest-users
mailing list