[Equest-users] Exterior Lighting Load
Jeremy Poling
jpoling at epsteinglobal.com
Mon Sep 14 08:06:56 PDT 2009
Jason,
I agree with Jonathan - this part of the wizard is not too helpful. I usually leave it set to the default and then when I am in the detailed edit mode I adjust it to the actual kW load for the design. If this is for an ASHRAE 90.1 Appendix G model, then I separately calculate the kW for the baseline model and input that.
The site lighting is tacked onto the meter in eQuest as a separate load with its own schedule. You'll need to adjust the total load there.
JEREMY R. POLING, PE, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jonathan Curtin
Sent: Monday, September 14, 2009 8:32 AM
To: Jason Wendel; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Exterior Lighting Load
Jason,
I believe I tested that out once and the W/SF is the building exterior wall area. I generally don't find this wizard screen all that helpful.
Jonathan M. Curtin, EIT, LEED® AP
Mechanical Engineer
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Wendel
Sent: Monday, September 14, 2009 08:30 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Exterior Lighting Load
In the DD Wizard, screen 23, it asks for the exterior lighting load in W/ft2. Where is it getting the square feet to determine the Watts? Is there a way to tell it how much area outside you're trying to light? If not, why is there a W/ft2 input?
-Jason
________________________________
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/cdb9ccae/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/cdb9ccae/attachment-0002.jpeg>
More information about the Equest-users
mailing list