[Equest-users] Chiller ROI - HELP!
Brett Sanicola
BSanicola at asbengineering.com
Thu Apr 1 13:23:05 PDT 2010
I reread your email and something you said struck a chord. I'm assuming
the default curve, which I'm currently using, falls off drastically at
part load. Hence the reason for my results. Am I assuming correct?
Also, how would I change the curve? Can I do that in the wizard or will
I need to access the detailed interface?
Respectfully,
Brett Sanicola
Engineer
ASB Engineering
(516) 785-4200
From: James Hansen [mailto:JHANSEN at ghtltd.com]
Sent: Thursday, April 01, 2010 4:02 PM
To: Brett Sanicola; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Chiller ROI - HELP!
KW/ton drops off with decreasing part load, and since the chiller isn't
always operating at ARI full load conditions, you can't just divide
total chiller energy consumption (in KWH) by the total cooling load (in
btu) and hope to get anywhere near the full load rated KW/ton.
As you go about this ROI study, make sure that when you are analyzing
your proposed chiller replacement, that you create a custom EIR vs PLR
curve based on manufacturer's data, otherwise you're using a default
DOE-2 curve that isn't necessarily correct.
Furthermore, to make the study worthwhile, the existing chiller model
really needs to be normalized as best as possible to actual building
operating conditions. You can get away without doing it for a simple
comparison, but it would be more accurate if you normalized to utility
bills.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brett
Sanicola
Sent: Thursday, April 01, 2010 2:38 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chiller ROI - HELP!
I've been attempting to calculate a simple ROI for a new 250 ton chiller
our client wants to install to replace his older chiller. I ran the
simulation for the default "high rise hotel" construction which, to my
luck, is quite similar to the actual building. The detailed results,
however, are not making sense to me. Specifically, when I look at
Equipment Loads and Energy Use for the Chiller, the Elec Use and Cool
Load don't coincide given the default Chiller efficiency of .67kw/ton.
For example they give a Chiller Elec Use of 535453 KWH and a Cool Load
of 3294 MBTU. However, according to my calculations, at .67KW/TON,
535453 KWH should give me closer to 9590 MBTU. I see most of the hours
are in part load range, but does the efficiency drop off that
dramatically at part load that it would explain the discrepancy? Which
numbers should I base my analysis on, the Cool Load number or the Elec
Use number.
Also, on the same page (Equipment Loads and Energy Usage), it gives me a
peak load of 2436 KBTU/HR. However, when I go to the section titled
"Building Peak Load Components" the peak cooling load is significantly
less (1619 KBTU/HR)
At this point, I have no idea what any number represents, since I don't
know how it was calculated.
I greatly appreciate any help! Thanks.
Respectfully,
Brett Sanicola
Engineer
ASB Engineering
(516) 785-4200
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100401/bd9f0f6f/attachment-0001.htm>
More information about the Equest-users
mailing list