[Equest-users] Water-Side Economizers
James Hansen
JHANSEN at ghtltd.com
Thu Apr 15 14:48:03 PDT 2010
Just set up a new chiller in your primary chilled water loop, and set it
to type "waterside economizer". Then create the associated pumps /
power consumption, and eQuest will automatically use this chiller (in
lieu of any powered chillers) whenever there is a possibility for
waterside economizer based on ambient conditions and required
temperature of chilled water loop to meet loads.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Thursday, April 15, 2010 4:46 PM
To: Jeff Ross-Bain
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Water-Side Economizers
Jeff,
if you have chilled water coils through your unit MZ unit and the
chilled water is coming from a chiller, then the water size economizing
function comes from the cooling tower that is connected to the chiller
which supplies the chilled water coils. If you are talking about
economizer --in general terms, then maybe you are trying to
air-economize which should be able to be input in the air-side
tab-cooling for your MZ AHU.
Look at the plant & cooling tower for your water econo inputs.
Pasha
On Thu, Apr 15, 2010 at 1:40 PM, Jeff Ross-Bain
<jross-bain at rbgreenbuilding.com> wrote:
Hi All,
I have an existing building with a multi-zone air handling system with
chilled water and hot water coils. The system consists of the air
handling units, a centrifugal chiller, cooling tower, and gas fired
boiler. I am trying to introduce a water-side economizer into the
system. In the detailed mode, I notice that a water-side economizer is
not allowed with a multi-zone system. The spreadsheet input simply has
an inaccessible "n/a" shown for the economizer and does not allow
access.
Am I missing something?
Thanks for your help.
Jeffrey G Ross-Bain, PE, LEED, BEMP
Ross-Bain Green Building, LLC
404-228-2893
P Build Green...Save Time
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100415/51c752e2/attachment-0001.htm>
More information about the Equest-users
mailing list