That is the answer i was expecting to here. thanks for your input
On Thu, Apr 22, 2010 at 12:27 PM, Bruce Easterbrook <bruce5 at bellnet.ca>wrote:
> That doesn't sound right. Poured concrete has an R-value around
> 0.08/inch. When "effective" is used commercially it normally is a hocus
> pocus addition for the mass effect but shouldn't be much more than 10%.
> eQuest would calculate it as a lag effect based on the mass, so a steady
> state value would be most appropriate.
> Bruce Easterbrook
>
>
> On 22/04/2010 10:38 AM, Rob Hudson wrote:
>
> When creating a model, i noticed that the R-value of the concrete i am
> using is the "effective" R-value, rated at 22. Should i use this or should
> i ask the concrete manufacturer for a steady-state R-value which will be
> much more accurate based on the materials?
>
> --
> Rob Hudson
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100422/1e9a33a6/attachment-0001.htm>
More information about the Equest-users
mailing list