Rob,
I believe you can use the Overall Design Flow (ASSIGNED-FLOW) at the zone level to set your maximum flow rate. It's in CFM not ACH but you can let eQuest do the math for you. In the "Edit/View User Expression" box enter: 12*#LR("SPACE","AREA")*10/60. Where 12 is your ACH rate (use a Global Parameter to make life easier when you start changing it in the parametric run) and 10 is your floor to ceiling height.
Matt Dubrovich, P.E.
LEED AP
EMC Engineers, Inc.
www.emcengineers.com<http://www.emcengineers.com/>
Making buildings work. Better.
(303) 974-1217 - direct
(720) 279-4426 - mobile
(303) 974-1239 - fax
Confidentiality Notice: This message and any materials attached are confidential, and are intended solely for the use of the addressee. If you are not the intended recipient, be advised that unauthorized use, disclosure, copying, or distribution is strictly prohibited. If you received this message in error please notify the sender and destroy your copy immediately.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Monday, April 26, 2010 6:51 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Air Change Rate Question
This should be a quick question, but with eQuest you never know.
I am trying to set my ACH rates to 12, and in an parametric run, turn it down to 6. This doesn't appear to be working because the entry line for the ACH is minimum air to the zone.
Is there a way to set the air flow to see the ACH minimum air as a maximum?
--