[Equest-users] Demand Controlled Ventilation
Bishop, Bill
wbishop at pathfinder-ea.com
Wed Apr 28 07:43:24 PDT 2010
Rob,
I recently modeled DCV successfully for the first time. (I showed
savings anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or
OA-FLOW/AREA. The OA flow/per (person) is what will get you the savings,
based on your occupancy schedule(s). I also created a MIN-AIR-SCH,
coinciding with the fan schedule, set to zero when fan is off and -999
when fan is on.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Wednesday, April 28, 2010 9:55 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Demand Controlled Ventilation
I am having some trouble with setting up DCV in my model. if i select
DCV in Zone Sensors for the Min OA Control Method and a min outside Air
Ratio, do i need any Zone level OA inputs?
Any help or insight as to what inputs are necessary for DCV would be
great!
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100428/4d0f59cd/attachment-0001.htm>
More information about the Equest-users
mailing list