[Equest-users] Sloped grade - partially underground walls
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Apr 29 06:51:43 PDT 2010
Chris,
You need to create a new polygon with the same width (x) and height (y)
of the existing wall. The new polygon will only have three vertices
instead of four. Create a second wall, using the same location as the
first wall (such as "V1 of Space Polygon") and using the new polygon.
Create another new polygon for the opposite triangle and apply that to
the existing wall.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris
Jones
Sent: Thursday, April 29, 2010 9:27 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Sloped grade - partially underground walls
How would one setup a partially underground wall. For example, the
spaces in question have two wall types on one face - a portion is
underground and a portion is above. These are two different wall
types and the grade slopes along the wall so the two walls are
trapezoidal in shape.
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100429/2089826d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20723 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100429/2089826d/attachment-0001.jpeg>
More information about the Equest-users
mailing list