[Equest-users] Active Chilled Beam/Fan Coil System
Bruce Easterbrook
bruce5 at bellnet.ca
Fri Apr 9 13:21:36 PDT 2010
Thanks John, chilled beams are also called induction diffusers.
Bruce
On 09/04/2010 03:59 PM, Grando, John wrote:
> Have you looked into SYSTEM TYPE = IU (Induction Unit). This may be a
> better path to try.
>
>
> *John Grando LEED AP| Mechanical Engineer
> *
>
>
> ------------------------------------------------------------------------
> *From:* Greg Collins [mailto:GCollins at glumac.com]
> *Sent:* Friday, April 09, 2010 2:00 PM
> *To:* Bruce Easterbrook
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Active Chilled Beam/Fan Coil System
>
> Bruce,
>
> I agree with your theory and the justification, but the question is
> ultimately "how to model it?" I don't think you can put in negative
> heat for a baseboard system, hook it up to a chilled water loop and
> get results you can count on.
>
> Greg
>
> *From:* Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
> *Sent:* Friday, April 09, 2010 8:59 AM
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Active Chilled Beam/Fan Coil System
>
> I'm not totally up on using DOAS with eQuest or with chilled beams
> being in Canada but it would seem to me the OA will have to be used to
> control humidity in the space. The chilled beam should not be used
> for latent cooling, sensible only, to prevent condensation issues.
> The DOAS will need to control the dewpoint of the room air and
> maintain it below the operating temperature of the coil in the chilled
> beam. The chilled beam would only be dealing with the sensible load
> from the space. The DOAS would do everything else. The question
> would be will eQuest allow a single zone AHU c/w economizer and a
> baseboard system with negative heat? I have never tried that with eQuest.
> Bruce Easterbrook
> Abode Engineering
>
> On 08/04/2010 04:46 PM, James Hansen wrote:
>
> I'm interested in this as well -- I know that in DOAS systems like
> active chilled beams, the primary air often takes on a fairly large
> chunk of space latent cooling, and if this can't be passed on from the
> DOAS system to the space, then I don't see how we can believe the results.
>
> *GHT Limited
> **James Hansen, PE, LEED AP*
>
> *Senior Associate*
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA 22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com <http://www.ghtltd.com/>
>
> * *
>
> *From:* equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Greg Collins
> *Sent:* Thursday, April 08, 2010 4:39 PM
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] Active Chilled Beam/Fan Coil System
>
> Hi all,
>
> I'm working on modeling an active chilled beam system. It consists of
> the chilled beams and a dedicated unit to provide primary air (mainly
> ventilation air) to the beams at 55 degrees. I've modeled the chilled
> beam system as a fan coil system, but am wondering about my options
> for modeling the primary air.
>
> My question is this: If I attach the primary/ventilation air unit to
> the fan coil system in the FC's Outdoor Air tab under "Outside Air
> from System" will the temperature of the air coming from that unit
> have an impact on the load in the space? I have a ton of hours at
> very low load during the winter months, and I want eQuest to use the
> 55 degree primary air as the first stage of cooling for the space and
> not "double up" the cooling energy by cooling the 55 degree air and
> then not use that for cooling in the zones.
>
> If anybody has some input, it would be appreciated.
>
> *Greg Collins*
> Design Engineer / Energy Analyst
>
> Mechanical Department
> LEED® Accredited Professional
>
> http://www.glumac.com/glumacsig.gif <http://www.glumac.com/>
>
> ------------------------------------------------------------------------
>
> NOTE OUR NEW ADDRESS
>
> 18200 Von Karman Ave., Suite 100
> Irvine, CA 92612
> T. 949.833.8190 F. 949.833.0252
>
> *Thinking. Inside the building.*
> www.glumac.com <http://www.glumac.com/>
>
> ------------------------------------------------------------------------
>
> The information contained in this communication is confidential, may
> be privileged, and is intended only for the use of the addressee. It
> is the property of GHT Limited. Unauthorized use, disclosure or
> copying of this communication or any part thereof is strictly
> prohibited and may be unlawful. If you have received this
> communication in error, please notify me immediately by return e-mail
> or by e-mail to ght at ghtltd.com <mailto:ght at ghtltd.com>, and destroy
> this communication and all copies thereof, including all attachments.
> Thank you.
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
> any) are intended solely for the use of the addressees hereof. In
> addition, this message and the attachments (if any) may contain
> information that is confidential, privileged and exempt from
> disclosure under applicable law. If you are not the intended recipient
> of this message, you are prohibited from reading, disclosing,
> reproducing, distributing, disseminating or otherwise using this
> transmission. Delivery of this message to any person other than the
> intended recipient is not intended to waive any right or privilege. If
> you have received this message in error, please promptly notify the
> sender by reply E-mail and immediately delete this message from your
> system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/363f070e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 6582 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/363f070e/attachment-0002.gif>
More information about the Equest-users
mailing list