I think you're just running into the default naming convention for
spaces above your conditioned zones in the wizards. If you check I
think you'll find they're unconditioned.
As long as you specify each airside system as "ducted" or "direct"
return, you should be modeling the intended behavior =). Dakota Kelley
did a fine job of nailing this topic down recently that I won't try to
outdo, so I've copied his email (and the preceding thread) below for
your perusal - this may not yet be in the archives as it popped up last
week.
Additionally, I'll continue to strongly suggesting all new eQuest'ers
bookmark these 2 mailing list archive search pages as a great primary
resource, if you haven't already:
http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Stephen
Sorensen
Sent: Monday, April 12, 2010 10:59 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 1st Time
Maybe I should have started with an easier model, but for my first real
crack at e-Quest, I am modeling a 3 story religious worship building. My
floor to floor height is 12' and my floor to ceiling height is 10'. All
return air is ducted. But, that unconditioned space shows as plnm even
though I specified that return air is ducted. Will this cause an issue
with my HVAC loads or is this normal?
Stephen Sorensen
Hansen Engineering
Friendsville, PA
P: 570-553-4284
F: 570-553-0234
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dakota
Kelley
Sent: Wednesday, April 07, 2010 9:58 AM
To: Katherine Roberts; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modelling plenums in eQUEST
Dr. Kat,
You are correct. I'm not sure how far into the rabbit hole you feel
like going, but let me add a couple additional points:
1) What you choose for "System per Area" in the Air-Side Wizard (Screen
1) will determine whether eQUEST creates one plenum per zone or one
plenum per floor. Selecting "System per Zone" results in one plenum
zone for each occupied zone (in addition to the system being replicated
for each specified zone, of course), and any of the other three options
result in one plenum per floor. This has implications for modifying
building geometry in the detailed interface in addition to return air
temperatures.
2) The difference between an unconditioned zone a plenum zone, as far as
eQUEST is concerned, is whether or not the zone is a return air path for
its parent system (assuming non-ducted return). Both are considered
unconditioned space types. So, for example, you could have a mechanical
room as a zone, specify it as a plenum, and its parent system will
consider that zone's temperature when determining the return air
temperature. Plenums do not necessarily have to be above-ceiling.
3) If you choose ducted return in the wizard, eQUEST will turn your
above-ceiling "plenum" into an unconditioned zone.
4) An unconditioned zone cannot have exhaust specified, but exhaust flow
and fan power, as well as a make-up air source, can be specified for a
plenum zone.
Thanks,
Dakota Kelley
Telios MEP Engineers
Dallas, TX
-----Original Message-----
From: Katherine Roberts [mailto:Katherine.Roberts at arup.com]
Sent: Wednesday, April 07, 2010 8:55 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modelling plenums in eQUEST
Equesters,
I'm new to eQUEST and want to check that I'm understanding it correctly
- am I right in assuming that you do not have to actually build the
plenums into the CAD model but just assign a plenum to a space i.e. by
using the floor to floor heights and floor to ceiling heights?
Thanks
Kat
Dr Katherine Roberts
Engineer
Environmental Physics London
13 Fitzroy Street
Arup W1T 4BQ
Tel: +0044 (0)207 755 5454
Internal freecall: 55454
www.arup.com
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100412/18c1ebc6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100412/18c1ebc6/attachment-0002.jpeg>
More information about the Equest-users
mailing list