Is an ASHRAE 62.1 analysis done and confirmed?
Bruce Easterbrook P.Eng.
Abode Engineering
On 30/07/2010 12:41 PM, Paul Diglio wrote:
> Vidya:
>
> You are welcome. Actually the response to your query was one reason I
> wrote the Administrator.
>
> My background is as a licensed HVAC contractor, mechanical designer
> and energy auditor/CEM/CEA/CBCP. I have audited many buildings and
> worked on multiple designs where a variable air volume air handler was
> existing or was specified without any VAV terminal devices.
>
> Usually the static pressure of the fan is reset based on a space
> temperature - discharge air temperature algorithm. In a typical
> investment grade audit, I will specify that a VFD be installed on the
> fan and that the CFM be reduced as the outside air temperature drops,
> since we do not need as much air for heating as for cooling.
> Remember, reducing the CFM of a centrifugal fan just 20% will reduce
> the kW input almost by half.
>
> It is not the best way to control a VFD, but it works, saves energy
> and has been approved on many occasions during the incentive review by
> the utility company PE. The sizable incentives that I have received
> for this strategy is indicative that it works. I have also returned to
> the site during the monitoring and verification phase and the energy
> savings have been confirmed.
>
> Good luck with eQuest,
>
> Paul Diglio
>
>
>
> --- On *Fri, 7/30/10, vidya gowda /<vidyacg at vt.edu>/* wrote:
>
>
> From: vidya gowda <vidyacg at vt.edu>
> Subject: Re: [Equest-users] eQuest Forum Courtesy
> To: "Paul Diglio" <paul.diglio at sbcglobal.net>
> Date: Friday, July 30, 2010, 12:17 PM
>
> thanks Paul,
>
> That was kind of you to ask on behalf of the mail equest and
> energy modeling users, without this list sometimes it becomes
> difficult to work on when you are on your own.. and when people
> comment that new users should first learn, this is one of our
> primary source of information, if we are not allowed how will we
> reach to the level where the established already are???
>
> Earlier today, I had personally appologized to all the people who
> has replyed to my query saying that next time I would not put up a
> question realted to design. But this surely is reconfirming.
>
> thanks it helps get some motivation instead of feeling low with
> such comments.
>
> Kind regards,
> Vidya
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100802/1ba3b7d3/attachment.htm>
More information about the Equest-users
mailing list