[Equest-users] Air Side Economizer savings
Fleming, Joe
joe.fleming at tlc-eng.com
Wed Aug 11 13:18:58 PDT 2010
Ok. Add Econo-Lockout and set it to yes. Then, when you are in the Parametric Run Definitions dialogue box, click on grid view and compare to the Baseline items.
For an accurate savings comparison, check to make sure Baseline has "NO" compressor lockout and your run says "YES". Also check to make sure the baseline OA control is set to "FIXED". (And you can compare other inputs to make sure you are comparing the two systems the way you want).
Can you email the grid view?
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer I
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image001.gif at 01CB3970.E6FC0EB0]<http://www.tlc-engineers.com/>
From: Sabesan, Anusha [mailto:asabesan at noresco.com]
Sent: Wednesday, August 11, 2010 3:56 PM
To: Fleming, Joe; equest-users at lists.onebuilding.org
Subject: RE: Air Side Economizer savings
Outdoor Air Vent &Economizer - OA Control - OA temperature
This is the parameter I changed. And then I also inputted DBT High Limit (65F) and DBT low limit (45F).
Thanks
Anusha
Anusha Sabesan
NORESCO
(m) (781)534-8296
(o) (508)614-1078
From: Fleming, Joe [mailto:joe.fleming at tlc-eng.com]
Sent: Wednesday, August 11, 2010 3:48 PM
To: Sabesan, Anusha; equest-users at lists.onebuilding.org
Subject: RE: Air Side Economizer savings
Which keywords did you adjust in your parametric component?
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer I
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image001.gif at 01CB3970.E6FC0EB0]<http://www.tlc-engineers.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sabesan, Anusha
Sent: Wednesday, August 11, 2010 3:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Air Side Economizer savings
I have been trying to model an existing building for which one of the parametric run being Air Side economizer savings. Every time (for different buildings) I do this run I come across negative savings. The building is located in New York. The system is a multi zone system. I hear that many people have across this situation. My cooling savings is also minimal. Am I doing something wrong?
Please advice.
Thanks
Anusha
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/fe3bf90e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/fe3bf90e/attachment-0001.gif>
More information about the Equest-users
mailing list