[Equest-users] Auto Auction - Conditioned Space?
Mehta, Gaurav
Gaurav.Mehta at stantec.com
Mon Aug 16 13:29:41 PDT 2010
Charles,
Is there a boiler providing hot water for the heated floor, or how is the floor heated?
Then check its output capacity.
According to ASHRAE Standard 90.1-2007, a space is considered a 'heated space' (conditioned space) if the system's output capacity relative to the floor area is greater than or equal to the criteria in the Table 3.1 shown below:
If the heating system's output capacity is greater than or equal to 3.4 Btu/h.ft2, and doesn't meet the criteria listed in Table 3.1, then the space may be considered a semi-heated space, otherwise, it will be considered as an unconditioned space.
Please refer to Section 3.2 Definitions of Standard 90.1.
Gaurav Mehta, LEED® AP
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com <http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Charles Welch
Sent: Monday, August 16, 2010 12:19 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Auto Auction - Conditioned Space?
I am modeling an Auto Auction which has open doors at each end for cars to be brought through.
There is no HVAC system, but the floor is heated.
Would this be considered a conditioned space for LEED or federal tax rebate purposes?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/07bed7b1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 16872 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/07bed7b1/attachment-0002.png>
More information about the Equest-users
mailing list