[Equest-users] question about performance curves
Jenny Zhang
jenny.zhang at arup.com
Thu Dec 9 23:08:25 PST 2010
Hi wanglin,
In eQuest to simulate the hourly performance of chillers 3 curves are used for calculation. You can find the different explanation by the paper ‘Tools and Techniques to calibrate Electric chiller component models’ in ASHRAE TRANSACTIONS( Also you could find the same material on WWW.ENERGYDESIGNRESOURCE.COM<http://WWW.ENERGYDESIGNRESOURCE.COM>)
The NPLV in defined when the chiller operating mode/the curve is in ARI 550 Rated condition. You can get enough testing data from manufacturers to make your curve.
Also it will be a risk if you change the curve without suitable testing data.
At last it is a safe way to use default curve to model an ASHRAE baseline because the default IPLV is a little higher than minimum requirement by ASHRAE 90.1-2007.
Jenny. Z
Shanghai ARUP
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of wanglin
Sent: 2010年12月10日 14:56
To: equest-users
Subject: [Equest-users] question about performance curves
In ASHREA, the part load performance of chiller is described by IPLV or NPLV.But in equest, it seems that the part load performance of chiller is described by performance curves. How do I edit the performance curves so that IPLV or NPLV prescribed in ASHREA are reflected in equest.
________________________________
网易163/126邮箱百分百兼容iphone ipad邮件收发<http://help.163.com/special/007525G0/163mail_guide.html?id=2716>
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101210/895c5cbc/attachment-0002.htm>
More information about the Equest-users
mailing list