[Equest-users] how to set the OA values in eQUEST
Grammy
grammy.hkust at gmail.com
Sat Dec 11 08:09:56 PST 2010
Dear Zhou,
OA can be inputed under the zone, which is conditioned by PTAC.
Referred to *<DOE2.2 Volume 3: Topics>*, Section AIRSIDE HVAC, SYSTEM TYPE =
PTAC, page 272, you can see that OA control is not under AC system, and on
page 273 and 274 there is an example input for this system: *OA control is
under zone control*.
After setting, you can output OA hourly data to check it works or not.
Regards,
Grammy
On Sat, Dec 11, 2010 at 11:27 PM, zhiren zhou <zhouzr at cabr-sh.com> wrote:
> Dear eQUESTers
>
> I am doing LEED-CS energy rating simulation. Part of the project is
> residential type (hotel) and the HVAC system for baseline is PTAC while the
> proposed system is FCU+DOAs. The Appendix G doesn’t tell us to create
> the PTAC baseline system with DOAS. But the question is how to set the OA
> value to PTAC system in eQUEST? I think I should set the OA value in the
> interface below, but how? Has anyone performed the PTAC simulation and Can
> you tell me the details or can you give me an example you did?
>
> Thanks a lot!
>
>
>
> Yours Zhiren Zhou
>
>
>
> [image: cid:image001.png at 01CB991B.D66A79A0]
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101212/522fbec4/attachment-0002.htm>
More information about the Equest-users
mailing list