[Equest-users] Does PTAC consumes less energy than FCU+DOAs?
Jenny Zhang
jenny.zhang at arup.com
Mon Dec 13 17:13:43 PST 2010
And I saw the cooling electrical input power in the third screen is green (default value). May be you should change it according to ASHRAE 90.1 minimum equipment efficiency.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook
Sent: 2010年12月13日 23:41
To: zhiren zhou
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Does PTAC consumes less energy than FCU+DOAs?
On your bottom screen adjust the throttling range, try 2 and 4. .3 is too tight, the system will fight itself.
Bruce Easterbrook
Abode Engineering
On 13/12/2010 08:52 AM, zhiren zhou wrote:
Dear all
Now I’m doing a LEED-CS energy simulation, part of the project is residential type and I use system 1(PTAC), and the proposed is FCU+DOAs. The results shows that the baseline is consume less energy.
So the question is: Does PTAC consumes less energy than FCU+DOAs?
Of course I’m not sure whether I has modeled the PTAC correctly. So I put some important images below. The cooling source is DX and the heat source is hot water loop. The supply fan is 0.0003Kw/CFM, and I keep the EIR default of 0.438 which is a low efficiency.
Could anyone tell me the cause or the mistake I’ve made? Thanks a lot!
Yours Zhiren Zhou
[cid:image001.png at 01CB9B6F.10DE4B70]
[cid:image002.png at 01CB9B6F.10DE4B70]
[cid:image003.png at 01CB9B6F.10DE4B70]
[cid:image004.png at 01CB9B6F.10DE4B70]
[cid:image005.png at 01CB9B6F.10DE4B70]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 89965 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 39575 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 46406 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 52982 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 46312 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101214/ce0daac4/attachment-0014.png>
More information about the Equest-users
mailing list