[Equest-users] OK, I give up !!!!!!!!!!!!!!!!!!!!!

Bishop, Bill wbishop at pathfinder-ea.com
Mon Feb 1 04:52:42 PST 2010


John,
 
The second DHW heater had an entered capacity of "0.000". I entered a
non-zero capacity and the DHW energy use jumped. (I assume you are
looking for energy consumption and not just what the loop loads are on
the PS-D report.)
 
As an aside, remember when entering capacities for boilers and DHW
heaters in eQUEST that the units "MBtu/h" are millions, not thousands of
BTU. (Or do you really have a DHW heater that needs 17,000 gpm? :-))
 
Regards,
Bill
 
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.         
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Sunday, January 31, 2010 9:29 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] OK, I give up !!!!!!!!!!!!!!!!!!!!!
 
I have two separate models, one without internal loads to a building
section, one adding load (including DHW) to the previously unconditioned
building section. I attached the .PD2 and .INP files for the "larger
load" model.
 
The added heating, cooling, lighting, and equip loads show up, but the
DHW load remains the same.
 
In this "larger model", I made a second DHW circulation loop, fired by a
2separate DHW heater. I even change the dirver for the heater location.
 
No change.
 
What, o eQuest word, am I missing ?
 
My humble thanks
 
John Aulbach
 
 
 