[Equest-users] WLHP & Lack of an ERV
Kevin Madison
kevinjm5000 at yahoo.com
Tue Feb 16 16:38:28 PST 2010
Instead of using the 'HP' system TYPE, try using the 'PSZ' or 'PVVT'
system TYPE. With HEAT-SOURCE = HEAT-PUMP and CONDENSER-TYPE =
WATER-COOLED (and connected to a LOOP of TYPE=WLHP) you will be
simulating a water source heat pump. These two system types support the
full DOE-2 ERV functionality.
Kevin Madison PE
Madison Engineering PS
444 NE Ravenna Blvd Suite 406
Seattle WA 98115
www.madisonengineeringps.com
On 2/16/2010 1:42 PM, O'Connor, Dennis CAR wrote:
>
> Fellow Equest-Users,
>
> I would greatly appreciate it, if someone would take a moment to
> explain the following:
>
> Why doesn't eQUEST allow airside heat recovery with water loop heat
> pumps? HAP does allow this type of application.
>
> I went through the archives and was unable to find an answer to my
> question.
>
> Does anyone know of a work around using a WLHP?
>
> Thanks in advance for taking the time to review my question,
>
> Dennis O'Connor
>
> Graduate Student at the University of Hartford
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100216/29a68ece/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13120 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100216/29a68ece/attachment-0002.jpeg>
More information about the Equest-users
mailing list