Vikram,
When you use a sizing ratio of 2, you're oversizing the system by 100%
while the loads stay at 1/2 of what they should be. This is not what you
want.
Depending on the system type, using a single unit with 52,000 cfm can
affect the results because of the different load diversity.
Kamel Haddad
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram
Sami
Sent: February 24, 2010 17:22
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] System multiplier
I'm modeling a building with multiple zones per floor. Each floor is
supplied by two identical air handlers supplying 26,000 cfm each. I
would like to model it as a single system. Should I:
1. Model a single AHU with 26,000 cfm and assign it a multiplier
of 2 (system sizing ratio)
2. Model a single AHU with 52,000 cfm without the sizing ratio
(sizing ratio 1).
3. Model both air handlers (would prefer not to).
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
Please visit our new website | www.lordaecksargent.com
<file:///\\www.lordaecksargent.com\>
P Think GREEN before you print.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100226/4632abca/attachment-0002.htm>
More information about the Equest-users
mailing list