[Equest-users] Cooling EIR and unit EER
Supriya Goel
supriyagoel at gmail.com
Wed Jan 13 15:22:04 PST 2010
Jacob
You're right, EIR is not equal to 1/(EER/3.14)
The equation used by eQuest for calculating EIR from EER is-
COOLING-EIR = (1/EER - 0.012167) / ((1 / 3.413) + 0.012167)
If you want more information, I could send you the document from where I got
this.
Regards
Supriya
On Wed, Jan 13, 2010 at 4:11 PM, Jacob Goodman <jacobg at lseng.com> wrote:
> How does eQuest calculate "cooling electrical input ratio" shown in
> detailed edit mode when you input an EER in the wizard? From a few checks
> I've done cooling EIR doesn't equal 1/(EER/3.413) as I would expect.
>
> Jacob
>
>